Hello all. I have an issue I have not been able to find an answer to online. I have a 1794-VHSC connected to a Contrologix PLC and a Sick incremental encoder. Everything works fine. I have a homing routine for setting a location of a device. I jog this device and have it scaled so that it is reading distance traveled. The issue I have is, for apparently no reason and at random times, the counter will read "0" as its position, requiring I run another homing sequence. I have tried a lot of different things to get it to intentionally write a "0" however, I can't do it. My preset is set and, as part of the homing sequence, it writes this value into the counter, after the home LS is made, then broke. Any ideas would be awesome. Thank you.
 
The first two suspects are a power cycle and an unintentional trigger of a Reset input.

Have you intentionally tested both of those ?
 
It is changing to zero randomly while powered up doing nothing?


I haven't seen that, but I never use the actual counter presets or controls for anything anymore after too many headaches.
Generally, I use a PMUL instruction with a small word size to generate a delta every scan, and add that into a separate register from the actual counter.
Also, by inhibiting the ADD instruction when the system is powering up, or in other instances I might desire, stray pulses and such are ignored.
 

Similar Topics

Hey Everyone, After reading a lot on this forum and elsewhere I see not many are fond of the 1794-VHSC module. I can see to a degree as I was...
Replies
3
Views
189
So I have a customer that wants to replace an outdated PLS (Programmable Limit Switch). The current system uses a resolver and 2 outputs in a...
Replies
2
Views
2,312
Hi all. This would be my first post on this forum, but i have so say i have been following it for quite some time and it has provided me with alot...
Replies
4
Views
3,219
  • Poll
I have a 1794-VHSC card (encoder counter card) connected to a 1794-ADN scanner module. When I try to add the module in the right slot in the ADN...
Replies
7
Views
5,854
1794-VHSC Flex IO module. I have a encoder with only 1 channel. So it has 3 wires: 24vdc, vdc common, Channel A. I hook it up and configure the...
Replies
18
Views
8,449
Back
Top Bottom