I have a 1769-SDN DeviceNet scanner attached to a MicroLogix 1500, flashing 75 63. (No traffic, node 63).

The highly suspect part is that the default node addess for this hardware is 63, and, according to the OEM documentation, the scanner should be 00. There is only ONE node of I/O, and its switches are set to 01.

The weird part is that I can change the code to 90 or 81 just by manipulating output image, word 0, bits 0, 1, and 2, which RUN, FAULT, or ?? the module. So, this tells me the module is seen by the processor, and reacting to the output image table.

Possibly cleared eeprom??
 
The module has somehow been set back to factory defaults. Error code 75 indicates an empty scanlist, and of course the default node address for any DeviceNet product is Node 63.

You can do this with a Reset service code, but I've never seen it happen just out of the blue.
 
I've the same issue.

What can I do in order to scanner add the only device that i have conneted to the network? If my only options is autoscan mode

Thanks.
 

Similar Topics

All Found myself in a situation where I need to flash the 1769_sdn Devicenet module from 2.002 to 4.004. I uploaded from the module but it has...
Replies
11
Views
2,419
I am working on upgrading a system with a ML1500 that uses a 1769-SDN DeviceNet Scanner to a CompactLocix L24ER-QB1B. Due to cost, I need to...
Replies
2
Views
1,415
Hi anyone, We have a DeviceNet scanner 1769-SDN that is putting out " 08... Er" on the display. Anyone know what that means? We are not able to...
Replies
4
Views
1,748
I am using CLX L35E PLC. There is a 1769-SDN module in slot 1 of this PLC. When I want to view the devices over RSlnx, all devices are displayed...
Replies
1
Views
1,542
Hello, I'm trying to replace a 1769-SDN devicenet scanner on a compactlogix system. The issue i'm having is when i replace the scanner and...
Replies
1
Views
1,897
Back
Top Bottom