1769-l16

RBergmann

Member
Join Date
Jun 2002
Location
California
Posts
258
Help. Perhaps you can help. I am trying to connect to a 1769-L16 with a USB cable. I’m not having any luck. New program, new controller. After download, I will be able to connect using Ethernet.
 
In the RSlogix you need to run the virtual back plan driver as well as the USB driver to com with it.
Thanks, I thought I had done that but apparently not. Now I get a message (after much DL activity) that the device is not in the proper mode to update the firmware. The PLC has v20, but my new software only supports v21. Any thoughts?

Along with other manufacturers of PLCs, I do a lot of RSLogix 500 projects, but not too much with RSLogix/Studio 5000.
 
Last edited:
Thanks, I thought I had done that but apparently not. Now I get a message (after much DL activity) that the device is not in the proper mode to update the firmware. The PLC has v20, but my new software only supports v21. Any thoughts?

Along with other manufacturers of PLCs, I do a lot of RSLogix 500 projects, but not too much with RSLogix/Studio 5000.

try using controlflash to flash the firmware. I just now tried to flash a brand new l71 using the prompt when first connecting over usb, which failed with the proper mode error that you mentioned. I rebooted it and used controlflash and it worked fine.
 

Similar Topics

I'm looking into the fault codes of a 1769-L16 the tag is Local:1:C.FaultMode. I know its simple and Im just overlooking the simple answer in the...
Replies
2
Views
1,007
Dear all, First post on the forum. my supervisor and I have a 1769-L16-B1BB acting up in the field. We decided to program and send an identical...
Replies
8
Views
2,443
Hi All, Got a project which has specifically called for a L16 compact logix, to control 11 motors, all using the E300 module. All was well and...
Replies
22
Views
7,231
I am using RSLgix 20.0 and RSLinx 2.59 When i try to connect to L16 controller i get the error "Attribute value not settable". In offline mode the...
Replies
0
Views
1,400
Does anyone know what the data transfer rate for this series of CompactLogix PLC's? 1769-L24ER-QB1B to be exact. Cheers.
Replies
1
Views
98
Back
Top Bottom