Processor Error Message:

G file configuration error.. user program G file size exceeds capacity of the module.

I cannot seem to find any data to suggest why this error is occurring.

any ides would be helpful đź“š
 
First, be certain that it's a 1746-HSCE, not a 1746-HSCE2. They are functionally similar, but have different configuration sizes and formats.

What is the size of the G-File that you've configured ?
 
Hi Ken,


Yes, this card is the HSCE, and not the latter. I cannot fully answer your question about the size of the G-file, as I am uncertain where to look. I am only parroting what I see in the processor error tab under fault conditions.



In setting up the card, I followed the manual to the best of my ability bit-setting the required parameters for configuration and set-up, but fear I may be missing something there.



My suspicion is that I have somehow missed a required setting and the system check-sum is kicking out this fault code. ???
 
To find G file length
I/O Configuration
Advanced Config on bottom left after module selected.
Not familiar with this module so can't give you a value to plug in.
 

Similar Topics

How do I keep track of the counts for this encoder in programming. I am using logics 500. The encoder PPR is 1000.
Replies
3
Views
2,915
I have a double end tennoner with a ball screw for opening and closing. On the back of the motor driven by a VFD there is a 100PPR differential...
Replies
8
Views
3,910
I had a 1746-HSCE go suspected bad. have to swap the card in the morning. Other than dip switch settings is there any configuration to do?
Replies
1
Views
1,039
Hi there, I have a machine where was a servo with extra encoder. That encoder had resolution 100ppr/5V. We did replace complet servopack (...
Replies
0
Views
960
I have a SLC 5/05 processor and I am trying to reference an output from a High speed counter card to be used elsewhere in the PLC. The output...
Replies
1
Views
1,650
Back
Top Bottom