0-10V signal splitter

kongshitt

Lifetime Supporting Member
Join Date
May 2011
Location
indianapolis
Posts
28
Were having some debate here at work about adding some passive monitoring to our primary drive system on our production line. We want to use the 0-10V signal from the frequency drive to monitor the amps the motor is using. The PLC is already using this signal, but the OEM doesn't want to give us access to the PLC to give us that as an output. The debate is whether or not we need a signal splitter, or if we can parallel the 0-10V signal. Im pretty sure we can just parallel the signal, but our other electrician swears we need a splitter.
 
You can just parallel the voltage Signal. Current on the other hand you need a splitter

You may or may not need an isolator when sharing a current signal. It all depends on if the various devices share a common ground reference, and have isolated inputs. There are MANY threads on this side that have thoroughly explored this.

The same goes for a voltage signal; if every piece of equipment that needs the signal shares a common reference, it will work fine. If the references are not connected, or if there is a potential difference between them, you risk erroneous readings and damaged inputs and outputs.

Safest bet is to use an analog isolator. You may not need it, but it doesn't hurt, and it may save you headaches and damaged equipment.

As an aside: time to start putting language in your Purchase Orders that OEM's must supply schematics and source code without password protection. You presumably paid for the machine - you own it. They owe you the info to do this via the PLC if you want to go that route.


-rpoet
 
Were having some debate here at work about adding some passive monitoring to our primary drive system on our production line. We want to use the 0-10V signal from the frequency drive to monitor the amps the motor is using. The PLC is already using this signal, but the OEM doesn't want to give us access to the PLC to give us that as an output. The debate is whether or not we need a signal splitter, or if we can parallel the 0-10V signal. Im pretty sure we can just parallel the signal, but our other electrician swears we need a splitter.


The answer to your question depends on the impedance of the two voltage inputs.
Basically if the output on the VFD has enough current to supply the two inputs it will work fine. If it doesn't you will get a lower voltage than expected.
But since we are only talking about two inputs it will likely work without any problems.

As mentioned above ground potential of the analog voltage needs to be considered. Many times both VFDs and PLCs have both isolated input and outputs in which case you just want to make sure you have the analog grounds connected.

Voltage signals are not suitable to run any distance so I hope everything is in the same cabinet. If it's not it would be much better to convert the 0-10V that you want to monitor into 4-20mA.
 
Last edited:
Thanks for the info folks.

I had read a lot on the 4-20mA and we had already looked at a signal splitter, but on closer inspection the signal from the drive is 0-10V. As far as install location and wiring to ensure we are using the same reference, that poses no problem at all. It will be installed 2-3' from the drive, in the same panel. As far as a slight voltage drop I am pretty sure we can just calibrate the signals to account for that.
 

Similar Topics

We have constructed a new vibrator control station with local pots on the panel and remote pots on a wireless system. We are running 6 AB 525...
Replies
5
Views
725
I am having an issue with speed variations on a Vacon X4 drive running a product pump and we are not sure how to verify what the problem is. The...
Replies
5
Views
1,640
We have a project that has existing proportional valves and joysticks that they're using. The customer wants to eliminate the controller/driver...
Replies
6
Views
1,758
Just asking for clarification here, but from my research all I need is a 500 ohm resistor across the AI and the common? Heres my schematic. I...
Replies
5
Views
2,590
Hi Everyone, Does anyone know any method or any device that I can use in order to amplify the 0-250mV signal to 0-10V signal to be feed into PLC...
Replies
12
Views
4,007
Back
Top Bottom