M340 ping function command

the18

Member
Join Date
Nov 2019
Location
Casablanca
Posts
18
Hello, can m340 ping other devices(pc stations to be specific) in the same network inorder to have the connection status)?.
 
There's no way that I know of to initiate a ping from an M340. Typically the computers must write a changing value to the PLC for the PLC to detect that they are active.

If the other nodes can act as Modbus TCP servers other options are available.
 
If you are using a noc or noe card I know there are status bits for individual nodes configured in the program
 