Watchdog between 2pcs S7-1200 over Ethernet?

MrQ

Member
Join Date
Feb 2005
Posts
236
Hi,

What is the easiest way to create a Watchdog between 2pcs S7-1200 over Ethernet?
 
Last edited:
Downside of Put/Get is it is one sided, so unless you document well inside the program, the data just sort of magically appears, or is used for no good reason. We often don't recommend put/get for this reason, but, to be honest, it kinda just works (as long as the connection info is valid).



I-Device is pretty straightforward to set up, and would be faster depending on how fast the watchdog needs to be (based on Profinet, could communicate every couple milliseconds if you want). Upside over put/get in many circumstances is that it has a bit more diagnostics, but for a watchdog, i guess the data itself is all the diagnostics you really need.
 
As mk42 pointed out, I-Device is the easiest and most robust. For the watchdog what I like to do is send either the clock byte MB0 (if it is setup) or send the millisecond clock. This way you know it should change every scan. I prefer this over the heartbeat approach since it takes two scans minimum for the heartbeat.

Here's a good link from DMC about I-Device
https://www.dmcinfo.com/latest-thinking/blog/id/8907/siemens-plc-communication-with-i-device

Otherwise here is one from Siemens.
https://cache.industry.siemens.com/...00558/v1/109741600_config_SharedDevice_en.pdf
 
Downside of Put/Get is it is one sided, so unless you document well inside the program, the data just sort of magically appears, or is used for no good reason. We often don't recommend put/get for this reason, but, to be honest, it kinda just works (as long as the connection info is valid).

The other big downside (though not very likely to happen) is that they always work even if the partner PLC is in STOP.

Although others use the pulsing bit, I prefer the rolling counter incrementing the received value and checking that it was incremented on the other end.
 

Similar Topics

Hello everyone, First I want to clarify, I am not actually installing an external watchdog timer on any equipment. I was drinking my coffee this...
Replies
6
Views
830
Hi, I have an issue with AB Redundant PLC which was running perfectly for several years and all of a sudden both PLC was showing fault and...
Replies
3
Views
2,715
Hi, I’m after a bit of advice on how to setup PLC watchdog alarm in FactoryTalk ME. I would like to monitor a register and alarm on if it doesn’t...
Replies
6
Views
1,900
Hi, I'm developing a routine to detect and clear a watchdog major fault in a ContolLogix PLC. The software has three tasks and six programs...
Replies
3
Views
2,490
In the past day, on our Panelmate, we've gotten several "Watchdog Time Out" notifications. Usually, they will clear by pressing the cancel...
Replies
2
Views
1,160
Back
Top Bottom