testing vfd

If, by inputs and outputs, you mean the AC 3 phase input terminals and the AC three phase motor connection terminals (outputs), then the procedure is quite simple.

Locate the DC bus terminals. Usually they are labeled + and - and are located on the power terminal strip.

With all power and wiring off the drive, you can check the input bridge diodes with an ohmmeter between the + bus and each of the input terminals. You should have near continuity in one direction and an open circuit in the reverse direction.

Repeat the same with the - bus and each of the three inputs. Again, you should see low resistance in one direction on all three and high resistance on all three in the opposite direction.

Except on the largest drives, the diodes will all be in the same block so, if you have one shorted or open, there is no need to go on. The block is bad and will need to be replaced. If the drive is 460V 50hp or smaller, it is probably not worth repairing.

To test the outputs, do the same thing as the input with the ohmmeter in both directions except here you should see an open circuit in both directions in all combinations on all terminals. Again, the output IGBT's are usually all together on one block so, if one is shorted, the whole block must be replaced.
 
heh... i just sent out a .75hp AB 160C drive to get repaired through a third party (applied industrial). still cheaper than a new one by their pricing scheme.

I always ignored the DC bus, so thanks for the info DickDV... good stuff. My approach has always been: Wires tight and in right place? Settings correct? still doesn't work? then give it the boot.
 

Similar Topics

Hello, I can test/check the diodes in a VFD if the VFD has DC bus terminals available. All of the VFDs I see sold today don't provide access to...
Replies
15
Views
5,701
Hello, I have an older 3-phase (400V), 3hp Siemens Micromaster VFD that I want to test to make sure it still works. I have access to 400V...
Replies
7
Views
4,177
Hi everyone, Got a new "Challenge" from my boss. Due to a mix up on a order I have a extra PowerFlex 755 VFD on hand. The boss has asked me to...
Replies
6
Views
2,710
Does anybody know of a lab with a dyno that can do testing on some 40HP drive and motor combinations? Stuff like: - For line voltage of 80-90%...
Replies
19
Views
5,499
I am working on setting up a Prosoft Datalogger model PLX51-DLplus-232. This unit will be collecting data from a SLC 5/05 on the DB9 port set to...
Replies
3
Views
133
Back
Top Bottom