Single End vs Differential Analog Inputs

jsock

Member
Join Date
May 2023
Location
Lakeland FL
Posts
14
I am converting a SLC 500 to a Compact Logix. I plan on using a Compact Logix 5380 with conversion Kit.
The problem is that the analog input cards do not support single ended inputs.
Can these be converted to differential inputs?single ended.PNG
 
It basically just means you will have a bunch of wires jumpering all the commons together on your 5069-IF8 module when you land "single ended" devices on it, and you may need to skip the conversion module on those cards and rewire directly to the new cards if your old card is, for example, a 1746-NI16.5069-IF8.png
 
Last edited: