SCADA with schneider PLCs

Moha

Member
Join Date
Dec 2005
Location
Cairo
Posts
3
I wanna carry out a system with SCADA to control 20 motor and display its status
the quistion is:
if i use TWIDO plc what is the requried converter to able me to connect to Ethernet,as i will connect the SCADA pc to the Ethernet by Ethernet communication card?!!
how can make the addressing in the Ethernet
 
Twido uses the standard Modbus communications in a two wire format. So any of the commonly available Modbus to ethernet convertors should work. Also there is now a Twido available with an integral ethernet port.
 
You could use Citect SCADA, since Schneider are in the process of purchasing that company. This system has good support for Modbus and Ethernet, and Modbus Ethernet.
You may even be able to get away without a converter.
 
GooD NewS, you don't need a converter for Twido since there's been embedded ethernet port on Twido (TWDLCAE40DRF). Contact your =S= rep. for detailed catalog.
 

Similar Topics

So i am developing a project on v8.1 The plc is a m340 I import my tag XSY file from the control expert software succesfully. Part of these tags...
Replies
2
Views
1,730
Hi all, I have a system running a Modicon M340 with Unity Pro and a Magelis Compact iPC with Citect SCADA v7.0 connected via a managed ethernet...
Replies
2
Views
2,996
Greeting, I am doing some investigations on which driver(s) support tag based addressing (eg. Pump001_Running) rather than DB or Modbus based...
Replies
4
Views
3,760
Dear fellows, I need to know what is the protocol which i can use in LS plc to make the schneider HMI and scada work with it . I have alot of...
Replies
0
Views
1,774
Hello, the system we use is Scada 7.5 series. We have usb key activ now we need additional key to make the system work, how do we solve this...
Replies
0
Views
48
Back
Top Bottom