I am working with an Emerson CPL410 PLC that is connected to a Siemens AI 8xU/I/RTD/TC ST (6ES7531-7K00-0AB0) via Profinet (and a Siemens Scanner and suitable GSD file of course).
My issue is how to configure an 4 wire PT100 analog input from within Proficy Machine Edition.
This card is an 8 channel, 16 bit analog card. I understand that when wiring it for a 4 wire PT100, each PT100 consumes a pair of channels (EG #0 and #1) - one channel (#1) is used to supply the current to the device and the second (#0) is used to sense the voltage. And the counts will come from the sense channel.
My problem is that in PME when I select channel #0 as being a 4 wire PT100, I can still independently configure channel #1 as any type of measurement input that is supported by the device.
I guess that if I select channel #0 as a 4 wire PT100 that the system will ignore any configuration for channel #1. But that is a huge assumption.
Does anyone have any experience with this? How should I configure channel #1?
And once again I have no physical hardware to test.
My issue is how to configure an 4 wire PT100 analog input from within Proficy Machine Edition.
This card is an 8 channel, 16 bit analog card. I understand that when wiring it for a 4 wire PT100, each PT100 consumes a pair of channels (EG #0 and #1) - one channel (#1) is used to supply the current to the device and the second (#0) is used to sense the voltage. And the counts will come from the sense channel.
My problem is that in PME when I select channel #0 as being a 4 wire PT100, I can still independently configure channel #1 as any type of measurement input that is supported by the device.
I guess that if I select channel #0 as a 4 wire PT100 that the system will ignore any configuration for channel #1. But that is a huge assumption.
Does anyone have any experience with this? How should I configure channel #1?
And once again I have no physical hardware to test.