So I have a sort of unique situation where I'm wanting to run a PF755 from the IO and over ethernet. Of course, this comes with it's own set of challenges. It's tied into a multi-stage exhaust fan system for some emergency equipment. I need the hard-wired system to over-ride ethernet commands, always. What really makes this a pain is that I can't necessarily count on an ethernet connection being present. I basically need the IO terminals to over-ride the EIP commands. I'm really trying my best to keep this system's wiring as close to the original as possible.

I have two interposing relays with two sets of contacts. Each one switches DI RUN and it's DI Speed Sel. One relay sets the drive's speed at 20 Hz, one sets the drive's speed a 60 Hz. When neither is made, the drive sits at Speed Ref A, which is the EENET port. Once one of them pulls in, it uses the appropriate speed reference.

There is an emergency over-ride, but it's only for a single speed. Parameter 172, manual would be good to force the IO terminals to override ethernet control, but it forces you to use the manual speed reference, and I need to use the DI Speed select.

When I started this, I spoke with Rockwell and was told that the IO terminals would always over-ride ethernet on Run level and 2-wire control. The issue is that without that run input made, the drive start is inhibited. I also tried to use an additional Run Enable terminal, but on 3-wire control, terminals have to be made and broken. I was also told that using 2-wire and run level, if I sent a stop command over ethernet, the drive would stop, but then take back off. This isn't true. Even on 2-wire control the DI for Run must be broken and then made again. I'm going to test again, but I believe if I'm using the Run bit over ethernet and I take it away with the DI Run made, the drive's speed reference won't update. Using the onboard relay isn't an option as the contacts aren't rated for such a low current and the extra failure risk isn't acceptable. I've spoken with four separate people from Rockwell support and have yet to get a good answer.

Devicelogix was suggested, and I've been thinking about ways to manipulate parameters. I'll certainly need to do some testing, but I'm wondering if there might be a way to ignore ethernet commands. I'm thinking perhaps I can mask off certain sources using the 32x parameters.

Initially, my plan was: have the drive sitting with no inputs made, starting with run level, use DI status to switch to run edge if no DI's are made, use ethernet control. This is actually not necessary, as the logic doesn't work the way I was informed.

Now I'm thinking about using device logix and the mask parameters:

On initial startup, use devicelogix to perform checks. "resting" state on the drive's configuration would be that ethernet is masked off and only DI logic commands are allowed. I can't mask a stop command, BUT I can use the RUN bit from the PLC, so a stop command wouldn't be necessary. If the PLC can't send a stop, it won't be an issue. I'll also mask off the drive's speed reference to the DI in it's resting state. If no inputs are made, then allow the ethernet speed reference. As soon as any input is made, disable it. There other issue I'll have to verify through testing is that I may have to stop the drive either before or after applying this masking.

What I'm going for here is predictability in how the drive will behave. I want to integrate it into our control system for monitoring and HMI control, but be certain enough about how the drive will be have, and that the IO will over-ride ethernet commands without actually doing this in the PLC. I also need to make sure that should the drive start up, it's going to run on the hardwired system as it should. When I agreed to tackle this, I honestly thought there would be a terminal I could assign to just pick a dominant logic source. There are certainly better ways to go about doing what they want with this system, but I'm in it now. Just typing this out has helped some, but I know there are some members here that might have ideas or suggestions.
 
As it is a 755, you can use the drives built in PLC it is called DeviceLogix and is in slot 14, I was once at a site that used at least 2 PF755's to run a slew on a dredger and you could run either VSD as a Master or a slave or by itself, all the code was done in DeviceLogix, with multiple IO cards in each VSD.
 
I've done a similar thing with a powerflex 525, but it was a while ago. From memory I used the purge function for the hardwired run controls. Search the relevant drive manual for purge and see if it helps you out
 
I've done a similar thing with a powerflex 525, but it was a while ago. From memory I used the purge function for the hardwired run controls. Search the relevant drive manual for purge and see if it helps you out
Yea, thanks for the info there, but that doesn't work as I need to set the frequencies with the digital inputs or from ethernet. You have to have a constant frequency for the emergency override.
 
I've done a similar thing with a powerflex 525, but it was a while ago. From memory I used the purge function for the hardwired run controls. Search the relevant drive manual for purge and see if it helps you out
Actually, thinking again about it, if I have to use device logix I can probably use the purge function and just use the digital inputs to set the speed reference in devicelogix.
 
That was one of my requirements, I set a digital input to be the purge function, and set the purge frequency to 50Hz. When you're running in purge mode, the purge frequency overrides the other speed references.

Again, this is all from a PF525, but I should imagine the 755 has at least passably similar functionality.
 
That was one of my requirements, I set a digital input to be the purge function, and set the purge frequency to 50Hz. When you're running in purge mode, the purge frequency overrides the other speed references.

Again, this is all from a PF525, but I should imagine the 755 has at least passably similar functionality.
It's multiple frequencies on the over-ride. That's what makes it a pain. The purge function doesn't give a method to change the frequency.
 
Ah, right, missed that part
That's alright though. When you brought that up I realized that if I have to use devicelogix anyway, I can simply use it to set the frequency based on the digital inputs. I'm going to try that first. I was looking at changing parameters and stuff anyway, It would be much easier to just change a single frequency. Much safer as well.

I think this whole system could have been engineered a little better, so my thought process is that if I don't go changing it functionally and swapping out a bunch of hardware, I bear a bit less responsibility should it go wrong.
 
Figured I would give an update on the emergency over-ride. It isn't available until firmware 14, and I'm unable to do a download for a while, so I'll probably take the bitmasking approach.

Actually, thinking about it now, I'm going to just add the new devices to the IO tree and inhibit the old ones, then deal with cleaning it up when we have down time.
 

Similar Topics

Hi I was wondering I need to update the firmware of a 755 inverter does the drive hold the program on the drive and just updates the firmware or...
Replies
5
Views
183
So I'm replacing a terminal block on the inverter board for a 755. I'm wondering if anyone knows what conformal coating would be best? I'm not...
Replies
1
Views
143
Powerflex 755, running 2 weeks, and faulting with code 17 input phase loss.
Replies
3
Views
230
Hi All, This is my first PowerFlex 755 drive setup and I am having an issue with when I start the drive it runs at my minimum speed 5Hz, but...
Replies
10
Views
438
Need some help trying to set the IP address in a Powerflex 755 with a 20-HIM-A3 installed. Drive has an embedded Ethernet card from the factory...
Replies
4
Views
265
Back
Top Bottom