Powerflex 525 reset meters over Ethernet

forqnc

Lifetime Supporting Member
Join Date
Jul 2009
Location
Elizabeth City
Posts
148
Hi All,
I am working on testing a project with a Powerflex 525, final project will be a 755, and I am trying to reset the Elapsed kWh meter over Ethernet.
I thought I would be able to add the parameter ResetMeters (A555) into Studio 5000, then move a 1 into the parameter then back to 0 but this does not work.
I also tried to enter a 1 into the controller tag, still does not work.
I see A555 change briefly to a 1 then back to 0 on the drive, but it is not resetting the meter.
If I changed A555 to 1 using the drive keypad it works.
When I do this using a Yasakawa drive, I set H5-11 to 1 so I do not need to send an Enter command when I change a parameter, does the Powerflex 525 have something like this?
Any assistance is appreciated.
 
You need to message the drive.

CIP generic, set attribute single 0x10, class 0x93, instance 555, attribute 0xA, source INT, source size 2.
 

Similar Topics

Hi, people I have a problem with the reset encoder routine. I can not reset encoder positions(parameters 376 and 377). I followed the manual and...
Replies
1
Views
3,129
Fairly new to the drive so apologise for the layman terms. Textile machine uses PF525 VFDs to control motors. The speed of the drive is currently...
Replies
5
Views
105
Hello, I'm hoping someone can help me with understanding how to set/change these data types. We recently swapped from Invertek to AB drives...
Replies
1
Views
120
All, I have a PowerFlex 525 driving an agitator motor. The goal is to have the agitator start automatically after a power loss or a comm loss. I...
Replies
2
Views
110
Hi to all. We need to change a bad powerFlex 525 to a new one. How do you save the configuration to install in the new one? Thank you all for...
Replies
5
Views
283
Back
Top Bottom