Power Flex 525

Join Date
Mar 2023
Location
Wyoming
Posts
4
I have a 5 Hp powerflex 525 that I am having trouble with an overcurrent fault. I am new to drives and don't understand all parameters. I have a pump that is being controlled by a motor starter feeding another pump being controlled by the powerflex. When I have the first pump running and start the second pump I get an overcurrent fault. If I take the first pump out of the picture I seem to run with no problem on the second pump with the drive. Is there a parameter that needs to change assuming that pump with the drive is trying to hold back and overloading the motor? The reason for the second pump is to try to keep a constant psi (running off a transducer) to speed up and slow down the motor. This is confusing I know but this is a set up that I was thrown into and told to make it work.
 
Just so I get this straight you have two pumps, A&B. A is started by a motor starter and runs at max speed. B is controlled by the PF525.

A feeds into B. If A is running when B is started, B will fault with overcurrent. If A isn't running, B starts just fine. Correct?
 
One thing to try is to enable "flying start" (parameter A545) on the drive. If the first pump is running, the second pump will be rotating because of the fluid flow. That can confuse the VFD, leading to an overcurrent fault.
 

Similar Topics

I have an issue with Power Flex 525 during running processing, the VFD stopped suddenly while the PLC and VFD connection ok, VFD does not have any...
Replies
1
Views
145
I am trying motor startup with pf525 drive by using wizard start over ethernet communication but during direction test it's showing control error...
Replies
3
Views
221
hello everyone. I have a 525 VFD that works, the screen shows the output voltage and the output frequency but in UVW I do not have voltage...
Replies
0
Views
203
I have this 525 that i am controlling it via ethernet. I needed to jog the drive using a start PB. when the button is pressed, the drive moves and...
Replies
6
Views
714
Hi All, While Replacing a VFD in breakdown condition which is the right and easy way to replace the drive quickly. We are working with Plant PAX...
Replies
3
Views
1,551
Back
Top Bottom