I am providing 24 volts on encoder input but getting the 24 volts on encoder output.The output voltage is not changing,so I want to ask what will be the fault.If I am not wrong is it circuit fault,If yes then please tell me what would be the fault in circuit..The encoder image is also attached..

Regards
Sohail.

encoder image.PNG
 
Yeah this encoder is NPN configuration,but the problem I am facing is the output voltage is not changing during rotating ,I am getting only fixed 24 volts on Encoder phase A,B and Z
 
1) If your'e measuring through Digital multimeter?
if yes! ithink you should try with oscilloscope.Digital multimeter cannot tell you about Pulses.
2) If you've tried to give inputs to PLC and checked that your'e getting Pulses?
if not getting Pulses then it is confirmed you have faulty one Encoder.
Just replace it.
I hope you've got the solution!
 
Where are you measuring the voltage? Put the output into a high speed counter on the PLC and then see if it pulses.
 

Similar Topics

Dear all PLC's master, I'm trying to connect CPM1A to rotary encoder (Omron E6B2) using PRV with this code (0 0 DM100), but i can't read the...
Replies
11
Views
6,183
Hi All, Need some help regarding MicroLogix 1400 HSC, Can I use Omron Encoder : E6B2-CWZ6C 600P/R... I badly need help.. Thank you very...
Replies
12
Views
4,350
hi i am a beginner, can any one help me to use encoder or a proximity counter to calculate the positioning of belts.
Replies
16
Views
6,667
Help needed, Is there anyone who ever write code for OMRON Rotary Encoder with MicroChip's PIC16Fxxx series. I'm seriously needed. Thompson Soe...
Replies
0
Views
3,462
Good Morning: Our company as a Miic Tube bender, dated 1991, which has several Omron Servo Motors. One of these, a R88M-H50030, 500 watt unit has...
Replies
5
Views
4,920
Back
Top Bottom