Hello all,
I'm having issues with a PID and trying to tune it. I just do not understand why my CV goes to 105 with the settings I have.
Config:
CV High Limit = 100%
CV Low Limit = 0%
Scaling:
Process variable unscaled and engineering unit min/max are equal.
Unscaled max = 17
Unscaled min = 0
Engineering Unit max = 17
Engineering Unit min = 0
CV max (100%) = 95
CV min (0%) = 70
So, with this setup I would expect the CV to range from 70 to 95. I is limited to 70 on the low end, but why am I getting a value of 105 on the high end?
This CV is not being set anywhere else.
I'm having issues with a PID and trying to tune it. I just do not understand why my CV goes to 105 with the settings I have.
Config:
CV High Limit = 100%
CV Low Limit = 0%
Scaling:
Process variable unscaled and engineering unit min/max are equal.
Unscaled max = 17
Unscaled min = 0
Engineering Unit max = 17
Engineering Unit min = 0
CV max (100%) = 95
CV min (0%) = 70
So, with this setup I would expect the CV to range from 70 to 95. I is limited to 70 on the low end, but why am I getting a value of 105 on the high end?
This CV is not being set anywhere else.