Hi All,

There are three Controllogixs control seperate units and communicate together, how can one PLC know another two plcs are in fault status? Thanks.
 
Hi All,

There are three Controllogixs control seperate units and communicate together, how can one PLC know another two plcs are in fault status? Thanks.
The easiest way would ne to set up a "heart beat" for each PLC and look for it from the other 2.
If you lose it, that means the PLC is faulted or at least stopped running its program.
 
but this way will also include the communication failure, it can not tell it's caused by PLC fault or communication network failure. Can I make a fault handler rountine and send a bit to another plc before this PLC go to fault mode?
The easiest way would ne to set up a "heart beat" for each PLC and look for it from the other 2.
If you lose it, that means the PLC is faulted or at least stopped running its program.
 
but this way will also include the communication failure, it can not tell it's caused by PLC fault or communication network failure. Can I make a fault handler rountine and send a bit to another plc before this PLC go to fault mode?
I'd use a GSV to monitor Comms failure for each PLC, remote adapter, etc..
I have no acess to my PC but in case no one jumps in (Ken Roach)I can dig up a setup for comms monitoring.
 
My question is if major fault happen, the PLC go to controller fault handler Task, Does the communication still works(major fault is not caused by Comm)? If the communication still works for some time, I can configure a routine in the fault handler to send a bit to other PLC via controlnet. Otherwise, I have a hard way to use a DO(Fault mode off, Program mode ON) and in this plc's program also energize this Do during plc running. The Other PLC us this DO as DI to know if this PLC is in Fault mode. How is that?
I'd use a GSV to monitor Comms failure for each PLC, remote adapter, etc..
I have no acess to my PC but in case no one jumps in (Ken Roach)I can dig up a setup for comms monitoring.
 
Don't try to use the fault handler to initiate a message. That's not the purpose of the fault handler.

Use a repeating timer to fire a MSG instruction from the "monitoring" controller to the "monitored" controller, as described in RA Knowledgebase article ID # 21989. This uses the "Get Attribute List" service to read values from the Device Identity object.

This will allow you to read the Run/Prog/Fault controller state and Rem/Remote/Prog keyswitch position from the remote controller.

If the Message instruction fails with a communication error, you know that there is a communications path problem between the controllers.
 

Similar Topics

Does anyone know of a way to detect if someone is online with the controller in ControlLogix (from logic) I'm thinking that maybe there is a CIP...
Replies
7
Views
419
Hi PLC people, think about this scenario: The PLC is somehow connected to the same network with the facilities` network. Then someone connects to...
Replies
2
Views
155
Hi all, I am trying to find a way of detecting a motor is not isolated before attempting to run an inverter. We would normally use a 4 pole...
Replies
19
Views
3,158
Hello everybody, I have a vendor system that has some remote monitoring (read only) and remote control (read/write) data that is available via...
Replies
7
Views
2,908
Replies
1
Views
1,238
Back
Top Bottom