ckchew666 said:
Does anyone know what's the input & output type of IO at the Siemens S5-95U? It has 16 DI & 16 DO.
They are 'normal' 24VDC sinking inputs and 24VDC sourcing outputs.
There are also a number of interrupt and counter inputs on one D-sub connector, and some analog i/o on another D-sub connector.
The interrupt and counter inputs can also be used as normal inputs. So when you check an old 95U for where its i/o are used, be sure not to miss the special i/o.
 
JesperMP said:
They are 'normal' 24VDC sinking inputs and 24VDC sourcing outputs.
There are also a number of interrupt and counter inputs on one D-sub connector, and some analog i/o on another D-sub connector.
The interrupt and counter inputs can also be used as normal inputs. So when you check an old 95U for where its i/o are used, be sure not to miss the special i/o.

Jesper, thanks for ur hints! Do you have any idea where normally ppl use the interrupt input & counter input at?
 
ckchew666 said:
Hi,

Thx for ur info, the CP1H can support max. how many IO points?

Total of 320 I/O. Both the CP1H CPU and Expansion Modules have 40 I/O [24 Inputs and 16 Ouputs]. A maximum of 7 Expansion modules can be added. Therefore 320 I/O max. [192 IN and 128 OUT].
The expansion modules are available in smaller I/O counts.
If you need more than I/O [especially if your I/O is distributed i.e. not in main control enclosure] you can use the Compobus-S Expansion module that will increase your I/O count still further with remote Compobus I/O units.

http://oeiweb.omron.com/DocumentLibrary.asp

Enter CP1h on second line - Manual is W450-E1-02
 

Similar Topics

We recently created a channel on YouTube about PLC Onron Training and the others . I am very happy to Share to the community...
Replies
0
Views
1,944
We have a PLC Siemens S7 300 CPU 315 DP, using NT631C-V2 Omron HMI via Siemens HMI Adapter. Now having problems with its HMI that can not connect...
Replies
1
Views
6,426
Hi I want to control omron f7 inverter with s7-300 plc with profibus. If someone made similar project, can u share? or some documents. I've...
Replies
10
Views
5,963
I would like to connect a touch panel from Siemens (TP27 10 inch) to a Omron CQM1 PLC. I have tried to make a cable for it but it is not...
Replies
1
Views
4,846
hello hai to every body i am working as a plc programmer ON gefanuc plc. I want to know the details about the siemens plc, modicon plc, omron...
Replies
3
Views
8,413
Back
Top Bottom