Good morning all,

I've got a customer in a bind. They, like many, got confused about Allen Bradley's EtherNet/IP protocol and assumed it was normal ethernet comms. They are attempting to pull motor control data from a ABB EIU32 universal motor controller into a S7-1500 PLC. I don't work much with Siemens, but after some Googling I found a document/example TIA Portal project with a “LCCF_CipClient" function block that is intended to read/write data between an S7-1500 and ControlLogix PLC. The FB asks for an IP address, rack and slot number to look for the Ethernet/IP data, with the EIU32 not being a PLC I'm worried this FB won't work correctly?

Prosoft card seems to be the best solution, but as always, time is a serious limiting factor and they can't wait for the hardware's long lead time. Anyone have any experience with a software solution? I don't have a physical S7-1500 or an EIU32 to bench test any of this with which is also adding to the difficulty.
 
Disclaimer: I am not an expert in Ethernet/IP.

If I understand what you write correctly, then there is no other Ethernet/IP Scanner, there is only the S7-1500 which must read data from the device.
If that is correct, the below link should work.
https://support.industry.siemens.com/cs/be/en/view/109782314
And you are on the wrong path if you are trying to make the S7-1500 a client.

Chapter 4.2 describes how you must manually setup the devices for which the S7-1500 must act as a scanner.
You have to read the relevant data from the devices EDS file and enter these at the corresponding DB addresses.
It does look a bit daunting though.

... too slow !
 
If I understand what you write correctly, then there is no other Ethernet/IP Scanner, there is only the S7-1500 which must read data from the device.

Correct. The 1500 needs to read/write data to/from the EIU32. The EIU32 communication interface enables the UMC100.3 Universal Motor Controller to work on an EtherNet/IP™ network.

Also, this is a super noob question, but I'm never too old to learn....What is an EDS file?
 
The ABB EIU32 is not Allen-Bradley, but ABB. It's a different company.


EDS is "Electronic Data Sheet" and is used by AB (Allen-Bradley/Rockwell) software to know what it's connecting to. The Siemens version is a GSD file. See if ABB offers an EtherNet/IP GSD for this device. That may make it easier to connect.


The ESD file may give you enough information to make a connection; I'm NOT experienced in using them in a Siemens environment, though.



It may end up being easier to add a ProSoft module (or similar)to interface between the devices.
 
The ABB EIU32 is not Allen-Bradley, but ABB. It's a different company.


EDS is "Electronic Data Sheet" and is used by AB (Allen-Bradley/Rockwell) software to know what it's connecting to. The Siemens version is a GSD file. See if ABB offers an EtherNet/IP GSD for this device. That may make it easier to connect.


The ESD file may give you enough information to make a connection; I'm NOT experienced in using them in a Siemens environment, though.



It may end up being easier to add a ProSoft module (or similar)to interface between the devices.

GSD is for Profinet, not Ethernet/IP.
EDS is for Ethernet/IP.

As suggested, it may be a better solution to get a Profinet adaptor for the ABB device.
What is the EIU32?

For the ABB ACS VSD’s, they have 2x versions of the Ethernet adaptor. One does all 3x protocols (MBTCP/EIP/Profinet) & the other does the single protocol only (technically 4x versions I guess )
 
GSD is for Profinet, not Ethernet/IP.
EDS is for Ethernet/IP.

...


Thank you for clarifying that. I haven't mixed brands very much between AB and Siemens and I always used a ProSoft or Red Lion device between them except for one time I used a Profibus Flex IO bus adapter. Good to know that GSD/EDS is protocol specific instead of PLC specific. I just learned something!
 
GSD is for Profinet, not Ethernet/IP.
EDS is for Ethernet/IP.

As suggested, it may be a better solution to get a Profinet adaptor for the ABB device.
What is the EIU32?

For the ABB ACS VSD’s, they have 2x versions of the Ethernet adaptor. One does all 3x protocols (MBTCP/EIP/Profinet) & the other does the single protocol only (technically 4x versions I guess )

Thanks for clearing up the GSD/EDS confusion. I agree, a Prosoft card would be much easier, but we can't find one available to fit the customer's schedule.

The ABB EIU is an ethernet interface that provides EtherNet/IP connectivity for the Universal Motor Controller UMC100.3. I made an error in the title, there is no Allen Bradley in the system. I wish I could edit the title of this post.

I'm trying to get the UMC100.3/EIU32 data via EtherNet/IP to the S7-1500
 
If you can get your hand on a Windows industrial PC (which have DIN rail and use SSD), or a Linux industrial PC or a RevolutionPi or its equivalent, you could get a CODESYS license for the system you choose and very easily you can make your gateway. This would require the additional PROFINET device IO license which is inexpensive. CODESYS supports EtherNet/IP scanner by default and its engineering tool is very good. You can easily register the EDS file in the CODESYS engineering tool and set the IO connection between the EtherNet/IP adapter and the CODESYS program. Map the EtherNet/IP IO data in some variables, and on the PROFINET side configure the CODESYS local Profinet IO device that will talk to the S7-1500. Once you get the connection with the S7-1500 all you will need is a simple program that writes data to EIP from the PROFINET data it gets from S7-1500 and vice-versa.
 
I would give it a go with the Siemens library blocks.
If you can get your hand on any S7-1500 CPU and any Ethernet/IP device, you can setup a test rig.
The principle is the same for a different Ethernet/IP device, so you can get a long way by a test like that even if the devices in the test are not 100% identical with the final ones.
 

Similar Topics

in allen bradley kinetix 300 drive first E31 error shows after resting drive E11 error occurs need solution to reset E11 fault code
Replies
2
Views
35
Hi, I have a ControlLogix system with 1756-IF16 analogue inputs. I can't scale the inputs at the card as there is a requirement to facilitate...
Replies
14
Views
407
Dear community, I am trying to find a tool for Allen-Bradley PLCs similar to SiVArch for Siemens PLCs to automatically generate faceplates and...
Replies
0
Views
110
Hi everyone, new to forum. Since very long time i having issue with 1734-AENT module, after some period of time its keep stuck in error (simmilar...
Replies
19
Views
764
Hello, I am new here. I am trying to find good places to sell some surplus items that I have that isnt through ebay. Does anyone have any sources...
Replies
6
Views
462
Back
Top Bottom