Use the CLR instruction on the CTU ACC. This will leave the CU bit set and reset the CTU ACC to 0.
XIC CTU.DN CLR CTU.ACC |
![]() |
![]() |
#18 |
Lifetime Supporting Member
|
Diagnosing the process, one scan at a time; see images below.
xxx.png yyy.png
__________________
i) Take care of the bits, and the bytes will take care of themselves. ii) There is no software problem that cannot be solved with another layer of indirection. iii) Measurement is hard. iv) I solemnly swear that I am up to no good ![]() |
![]() |
![]() |
#19 |
Lifetime Supporting Member
|
Hmm, maybe Logix 5000 is different from MicroLogix:
__________________
i) Take care of the bits, and the bytes will take care of themselves. ii) There is no software problem that cannot be solved with another layer of indirection. iii) Measurement is hard. iv) I solemnly swear that I am up to no good ![]() |
![]() |
![]() |
Bookmarks |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Micro 850 Accumulator reset | Jody Collins | LIVE PLC Questions And Answers | 0 | February 8th, 2017 10:20 AM |
Mitsubishi Beginners question - System Reset | DecrepitDragon | LIVE PLC Questions And Answers | 4 | June 1st, 2015 10:06 AM |
Mitsubishi F1 series counter question. | Tharon | LIVE PLC Questions And Answers | 4 | March 5th, 2015 04:48 PM |
Manual vs. Automatic Reset | jrexrode | LIVE PLC Questions And Answers | 14 | January 20th, 2015 05:49 PM |
RSLinx and yellow question marks. | johnmac | LIVE PLC Questions And Answers | 2 | October 14th, 2014 12:32 PM |