SIEMENS PROFIBUS DP Networking

sherman4

Member
Join Date
Jun 2002
Posts
46
Hello all!

I have a Siemens S7-314C 2DP Controller and I would like to network this DP Master with 4 (four) Yaskawa Frequency Drives which are DP slave enabled.

How can I just add Drives which are not Siemens products to my Profibus Network using the S7 Simatic Manager Hardware Cofiguration?

I assume that because Profibus DP is a standard, I must be able to communicate a Siemens DP Master with any other DP Slave from any vendor.

Please confirm and indicate how to install the Drives GSD on the Hardware config for S7-314C 2DP

Thanks for the Help.
 
Double click Option after you have opened the hardware config , then you can Instal New GSD file , which will find itself in Additional Field Devices if your ctrl^K ,
don't forget to compile and save any changes . Take a not of the PIW and PQW for the device , then you can play with ladder and get it to go round and round
 

Similar Topics

I'm just trying to figure out the right method of adding a DO card to an existing rack. It's not the *next* open slot, but I have to move the AO...
Replies
5
Views
545
Kindly, we are trying to go online on an S7-300 plc, with profibus communication, using a CP5711 adapter. But when we open the Ladder and press...
Replies
0
Views
778
I'm trying to figure out how to read the actual speed reference value from the move blocks, writing to a DB that is being sent to the VFD. For...
Replies
5
Views
2,630
I have a piece of equipment with control split between two PLCs. A quantum 434, and a Siemens S7-300, communicating via profibus. I have a prosoft...
Replies
14
Views
5,241
Dose anyone have experience with Beckhoff FC3121 profibus master PCIe card connected to Siemens CP342-5 as a profibus slave? The data retrieved...
Replies
17
Views
4,784
Back
Top Bottom