#1 |
Lifetime Supporting Member
![]() ![]() Join Date: Oct 2021
Location: Penrith NSW
Posts: 21
|
![]()
hi guys, i need 2 diffirent brands to report to each other
the first is a AB Micro850 with 2080-OF2 for 4-20Ma output the second is Clickplc input 4-20Ma the old AB needs to report its levels to the new ClickPLC due to distance 4-20ma is the best option as its only 1 level sensor reading now wiring for the AB is common and C0 Terminal does the AB output its own Power source from the AB PLC or do i still need to get 24V dc to the terminals ? and which would be which ? i have tried 24V dc to Common - and out from C0 to the new PLC - but that shorts the 24Vdc Power supply the Recieving PLC is 0V Common and 24V dc + in from the transmitting 4-20ma device how do i wire the outputs from the AB to the new PLC |
![]() |
![]() |
#2 | |
Member
![]() ![]() Join Date: Nov 2016
Location: Fields of corn
Posts: 2,562
|
Quote:
when in doubt, I usually take a multimeter and measure if the input channel is giving out voltage. Have you tried that on both ends? Rockwell's manuals tend to be really good at wiring examples for what their IO can do. Page 10 of this manual has the two possibilities. The question is what is the other PLC expecting. https://www.routeco.com/en-gb/resour...anual_2080-OF2 Also, because of the distance, the question is somewhat moot. I'd put in a galvanic isolator in the middle just to ensure I don't get reference issues. |
|
![]() |
![]() |
#3 |
Member
|
I would use an isolator in the middle just for the sake.
__________________
My two cents. |
![]() |
![]() |
#4 |
Lifetime Supporting Member
![]() ![]() Join Date: Oct 2021
Location: Penrith NSW
Posts: 21
|
Thanks for the replies
appears the AB has its voltage already, and the Click needs the voltage seperate . so i may need an isoalter in between them any recomendations for devices to use as in isoalter between the two ? |
![]() |
![]() |
#5 |
Lifetime Supporting Member
|
I have a customer with an electroplating line that uses 90 signal conditioners, and they shopped around a lot for the most economical as they seemed to be replacing at least 1 every week.
They introduced me to PR Electronics that they started using for this and all other signal conditioner needs. Their universal transmitter takes mA, VDC, thermocouples, RTD's, potentiometer's and more inputs and has programmable outputs with programmable ranges. They are very competitive priced and I use them.
__________________
ivanovaautomation.com Some Jobs Are Best Started With A Sawzall And A Dumpster On Castors |
![]() |
![]() |
#6 |
Lifetime Supporting Member + Moderator
|
I have done it before.... not a 800 to Click but I went from a S5 to a SLC and it worked perfect, if you have the time (I did not) I would use a signal conditioner AD sells them
https://www.automationdirect.com/adc...l_conditioners
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, MicroLogix, ControlLogix, Siemens, Allen Bradley and more...OEM and aftermarket supplies... Aftermarket 1784-U2DHP Allen Bradley USB to DH+, new USB to 485 modbus |
![]() |
![]() |
#7 |
Member
![]() ![]() Join Date: Dec 2010
Location: Harrisonburg, VA
Posts: 828
|
You mentioned that the 4-20mA is better due to the distance between the PLCs. Are they (or can they be) on the same network? I bet Automation Direct would help you set up a messaging scheme between them so you could get the data across without analog signals at all.
|
![]() |
![]() |
#8 | |
Lifetime Supporting Member
![]() ![]() Join Date: Jul 2016
Location: Manchester
Posts: 460
|
Quote:
Quite handy as a lot of them can be gotten with a basic digital output screen, that shows the raw values being received/output. Helps with troubleshooting.
__________________
|
|
![]() |
![]() |
#9 |
Member
|
I would also recommend Acromag isolators without hesitation. Not sure how available they are in Australia, but I find them very easy to configure and haven't had one fail on me yet.
|
![]() |
![]() |
#10 |
Supporting Member
![]() ![]() Join Date: Nov 2018
Location: Scranton,PA
Posts: 155
|
|
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
RSLogix 500 - I/O mapping question | toads | LIVE PLC Questions And Answers | 8 | September 25th, 2019 01:40 PM |
Phoenix Contact PLC Analogue input card | Jayden | LIVE PLC Questions And Answers | 1 | July 25th, 2016 12:03 PM |
I want to run PLC on bench with an incorrect input card | realolman | LIVE PLC Questions And Answers | 11 | February 26th, 2014 03:34 PM |
Proximity Switch to PLC Input | narcilla | LIVE PLC Questions And Answers | 0 | March 19th, 2010 04:53 PM |
Real World Problem | Vietnam Bob | LIVE PLC Questions And Answers | 8 | November 23rd, 2002 04:03 PM |