Tachometer to Siemens PLC input

I have a fan motor with a tach out. How do I connect to a Siemens PLC ?
I have attahced the wiring diagram from Motor Manufacturer.I was thinking 24v to grey, wht to plc pnp input, (high speed module?) I only want to verify it's running
Attached Images
File Type: png Fan Motor2023-09-22 092127.png (196.7 KB, 46 views)

Last edited by KatSpike; September 22nd, 2023 at 10:42 AM.
  Reply With Quote
Old September 22nd, 2023, 10:39 AM   #2
mk42
Lifetime Supporting Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 3,150
I'd wire that 0-10V signal to an analog input module.
  Reply With Quote
Old September 22nd, 2023, 10:46 AM   #3
KatSpike
Member
United States

KatSpike is offline
 
Join Date: Sep 2023
Location: Michigan
Posts: 3
I wasn't sure if that was a 0-10V output, or if that was for me to supply 0-10v for speed control. That was my first thouight to go to analog input module.

Last edited by KatSpike; September 22nd, 2023 at 11:19 AM.
  Reply With Quote
Old September 22nd, 2023, 11:06 AM   #4
mk42
Lifetime Supporting Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 3,150
Quote:
Originally Posted by KatSpike View Post
I wasn't sure if that was a 0-10V output, or of that was for me to supply 0-10v for speed control. That was my first thouight.

My thought is that if it's just a motor, it won't have speed control built in. That would be part of the VFD. Motors do relatively often come with encoders/tachometers/etc as feedback to the PLC.
  Reply With Quote
Old September 22nd, 2023, 11:38 AM   #5
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: ᚴᚬᛒᛅᚾᚼᚬᚠᚾ
Posts: 16,131
The text "SPEED SETTING WITH FIXED OR VARIABLE RESISTOR" hints at that it does have an integrated speed controller. Or maybe it is just a simple DC motor.
I think that the fan receives up to 10V, anything less than 10V reduces the speed. The resistor and the PWM output is just another way to generate a voltage less than 10V.

The real question is what is the frequency of the tacho output. If it is not so high, you can possibly connect it directly to a regular PLC input. If it is relatively high, then you may have to use a dedicated counter card.
__________________
Jesper
NOTICE:
JesperMP has passive-aggressive tendencies, can be impolite and may even use sarcasm !
Also: ᛁᚠ ᚢᚬᚢ ᚴᚬᚾ ᚱᛅᚬᛏ ᚦᛁᛋ ᚦᛅᚾ ᚢᚬᚢ ᚼᚬᚠᛅ ᚴᚬᛁᚾᛅᛏ ᛘᚢ ᚱᛅᛋᛒᛅᚴᛏ
  Reply With Quote
Old September 22nd, 2023, 11:42 AM   #6
KatSpike
Member
United States

KatSpike is offline
 
Join Date: Sep 2023
Location: Michigan
Posts: 3
Motor Data
2920 RPM, 120vac motor

Last edited by KatSpike; September 22nd, 2023 at 11:45 AM.
  Reply With Quote
Old September 22nd, 2023, 11:56 AM   #7
JesperMP
Lifetime Supporting Member + Moderator
Denmark

JesperMP is offline
 
JesperMP's Avatar
 
Join Date: Feb 2003
Location: ᚴᚬᛒᛅᚾᚼᚬᚠᚾ
Posts: 16,131
Assuming the fan outputs one impulse per revolution, that will give you an impulse every 20 ms.
Assuming the pulse and pause are symmetrical, you need to sense the signal at ~7 ms or better. So you need an input that updates its inputs for both on and off transitions faster than 7 ms.
The PLC must update its program scan faster than the 7 ms, or the input must trigger a hardware interrupt.

edit: So you need to check if the above assumptions are correct.
__________________
Jesper
NOTICE:
JesperMP has passive-aggressive tendencies, can be impolite and may even use sarcasm !
Also: ᛁᚠ ᚢᚬᚢ ᚴᚬᚾ ᚱᛅᚬᛏ ᚦᛁᛋ ᚦᛅᚾ ᚢᚬᚢ ᚼᚬᚠᛅ ᚴᚬᛁᚾᛅᛏ ᛘᚢ ᚱᛅᛋᛒᛅᚴᛏ
  Reply With Quote
Old September 22nd, 2023, 01:10 PM   #8
parky
Member
United Kingdom

parky is offline
 
parky's Avatar
 
Join Date: Oct 2004
Location: Midlands
Posts: 5,484
And it's NPN so need to take that into consideration if using pulse output.
i.e. sink.
  Reply With Quote
Old September 22nd, 2023, 01:56 PM   #9
drbitboy
Lifetime Supporting Member
United States

drbitboy is online now
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 7,296
https://puhallinverkkokauppa.fi/files/pdf/53/L02-A1.pdf?


To be pedantic, I suspect OP actually wants to verify that (cooling?) air is flowing; detecting motor rotation may be good enough as a proxy but it is not, strictly speaking, a guarantee of same. That said, assembling a reliable airflow telltale sensor is a non-trivial exercise, and detecting motor rotation is probably the next best choice.

I worked with a group in a nuke plant managing computers and other electronic hardware for a while; one experienced engineer reflexively held his hand by equipment fans' exhausts every time he entered a room.
__________________
_
Brian T. Carcich
i) Take care of the bits, and the bytes will take care of themselves.
ii) There is no software problem that cannot be solved with another layer of indirection.
iii) Measurement is hard.
iv) I solemnly swear that I am up to no good
v) I probably have the highest ratio of forum posts to actual applications in the field (but no longer ∞ ).
vi) Hakuna matata.
vii) Bookkeeping.
viii) But I should be ignored.
  Reply With Quote
Old September 22nd, 2023, 04:01 PM   #10
mk42
Lifetime Supporting Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 3,150
Quote:
Originally Posted by mk42 View Post
My thought is that if it's just a motor, it won't have speed control built in. That would be part of the VFD. Motors do relatively often come with encoders/tachometers/etc as feedback to the PLC.

welp, nevermind, maybe I should read the dang print next time....
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Mitsubishi Robot comm. with Siemens PLC pacak LIVE PLC Questions And Answers 1 February 17th, 2020 10:24 AM
RSLogix 500 - I/O mapping question toads LIVE PLC Questions And Answers 8 September 25th, 2019 01:40 PM
Siemens or Omron? Gromit LIVE PLC Questions And Answers 35 November 14th, 2017 11:44 AM
writing in Periperal input address in siemens plc IJK LIVE PLC Questions And Answers 4 May 31st, 2011 08:27 AM
Siemens PLC PID Problem dutchkg LIVE PLC Questions And Answers 0 October 21st, 2008 07:11 PM


All times are GMT -4. The time now is 12:18 PM.


.