Tachometer to Siemens PLC input
I have a fan motor with a tach out. How do I connect to a Siemens PLC ?
I have attahced the wiring diagram from Motor Manufacturer.I was thinking 24v to grey, wht to plc pnp input, (high speed module?) I only want to verify it's running Last edited by KatSpike; September 22nd, 2023 at 10:42 AM. |
![]() |
![]() |
#2 |
Lifetime Supporting Member
![]() ![]() Join Date: Jun 2013
Location: MI
Posts: 3,150
|
I'd wire that 0-10V signal to an analog input module.
|
![]() |
![]() |
#3 |
Member
![]() ![]() Join Date: Sep 2023
Location: Michigan
Posts: 3
|
I wasn't sure if that was a 0-10V output, or if that was for me to supply 0-10v for speed control. That was my first thouight to go to analog input module.
Last edited by KatSpike; September 22nd, 2023 at 11:19 AM. |
![]() |
![]() |
#4 | |
Lifetime Supporting Member
![]() ![]() Join Date: Jun 2013
Location: MI
Posts: 3,150
|
Quote:
My thought is that if it's just a motor, it won't have speed control built in. That would be part of the VFD. Motors do relatively often come with encoders/tachometers/etc as feedback to the PLC. |
|
![]() |
![]() |
#5 |
Lifetime Supporting Member + Moderator
|
The text "SPEED SETTING WITH FIXED OR VARIABLE RESISTOR" hints at that it does have an integrated speed controller. Or maybe it is just a simple DC motor.
I think that the fan receives up to 10V, anything less than 10V reduces the speed. The resistor and the PWM output is just another way to generate a voltage less than 10V. The real question is what is the frequency of the tacho output. If it is not so high, you can possibly connect it directly to a regular PLC input. If it is relatively high, then you may have to use a dedicated counter card.
__________________
Jesper ![]() NOTICE: JesperMP has passive-aggressive tendencies, can be impolite and may even use sarcasm ! Also: ᛁᚠ ᚢᚬᚢ ᚴᚬᚾ ᚱᛅᚬᛏ ᚦᛁᛋ ᚦᛅᚾ ᚢᚬᚢ ᚼᚬᚠᛅ ᚴᚬᛁᚾᛅᛏ ᛘᚢ ᚱᛅᛋᛒᛅᚴᛏ |
![]() |
![]() |
#6 |
Member
![]() ![]() Join Date: Sep 2023
Location: Michigan
Posts: 3
|
Motor Data
2920 RPM, 120vac motor Last edited by KatSpike; September 22nd, 2023 at 11:45 AM. |
![]() |
![]() |
#7 |
Lifetime Supporting Member + Moderator
|
Assuming the fan outputs one impulse per revolution, that will give you an impulse every 20 ms.
Assuming the pulse and pause are symmetrical, you need to sense the signal at ~7 ms or better. So you need an input that updates its inputs for both on and off transitions faster than 7 ms. The PLC must update its program scan faster than the 7 ms, or the input must trigger a hardware interrupt. edit: So you need to check if the above assumptions are correct.
__________________
Jesper ![]() NOTICE: JesperMP has passive-aggressive tendencies, can be impolite and may even use sarcasm ! Also: ᛁᚠ ᚢᚬᚢ ᚴᚬᚾ ᚱᛅᚬᛏ ᚦᛁᛋ ᚦᛅᚾ ᚢᚬᚢ ᚼᚬᚠᛅ ᚴᚬᛁᚾᛅᛏ ᛘᚢ ᚱᛅᛋᛒᛅᚴᛏ |
![]() |
![]() |
#8 |
Member
|
And it's NPN so need to take that into consideration if using pulse output.
i.e. sink. |
![]() |
![]() |
#9 |
Lifetime Supporting Member
|
https://puhallinverkkokauppa.fi/files/pdf/53/L02-A1.pdf?
To be pedantic, I suspect OP actually wants to verify that (cooling?) air is flowing; detecting motor rotation may be good enough as a proxy but it is not, strictly speaking, a guarantee of same. That said, assembling a reliable airflow telltale sensor is a non-trivial exercise, and detecting motor rotation is probably the next best choice. I worked with a group in a nuke plant managing computers and other electronic hardware for a while; one experienced engineer reflexively held his hand by equipment fans' exhausts every time he entered a room.
__________________
_ Brian T. Carcich i) Take care of the bits, and the bytes will take care of themselves. ii) There is no software problem that cannot be solved with another layer of indirection. iii) Measurement is hard. iv) I solemnly swear that I am up to no good ![]() v) I probably have the highest ratio of forum posts to actual applications in the field (but no longer ∞ ![]() vi) Hakuna matata. vii) Bookkeeping. viii) But I should be ignored. |
![]() |
![]() |
#10 |
Lifetime Supporting Member
![]() ![]() Join Date: Jun 2013
Location: MI
Posts: 3,150
|
|
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Mitsubishi Robot comm. with Siemens PLC | pacak | LIVE PLC Questions And Answers | 1 | February 17th, 2020 10:24 AM |
RSLogix 500 - I/O mapping question | toads | LIVE PLC Questions And Answers | 8 | September 25th, 2019 01:40 PM |
Siemens or Omron? | Gromit | LIVE PLC Questions And Answers | 35 | November 14th, 2017 11:44 AM |
writing in Periperal input address in siemens plc | IJK | LIVE PLC Questions And Answers | 4 | May 31st, 2011 08:27 AM |
Siemens PLC PID Problem | dutchkg | LIVE PLC Questions And Answers | 0 | October 21st, 2008 07:11 PM |