Old September 20th, 2023, 02:38 PM   #1
Shimmy
Member
United States

Shimmy is offline
 
Join Date: Sep 2023
Location: USA
Posts: 4
Greetings Controllogix 5561 176-L61B data restore

Hello all first time user here with a question about how to repopulate data on my controllogix 5561 176-L61B. Combination of a low PLC battery and power outage corrupted or erased my PLC data.

I am an owner/operator and not educated in PLC programing yet. The machine the PLC lives in has a PC that came with the unit when I purchased it that displays factory talk interface. I looked through the cabinet for a disk or thumb drive. I think the data file is saved on the PC (*ACD file?) as well as the program I will need to reupload the PLC info from the pc.

Will an intensive class on PLC's be what I need to go through to gain the knowledge to re upload the data?

I have gone to manufacturers of the machine and as well as AB and Rockwell/ Bosch. I have been given the full ghost going on my 3rd month.

I guess I need to know where to start with my issue and I have been directed here by TW Controls.

Any help will be appreciated.
  Reply With Quote
Old September 20th, 2023, 02:42 PM   #2
glenncovington
Lifetime Supporting Member
United States

glenncovington is offline
 
glenncovington's Avatar
 
Join Date: Apr 2002
Location: Gloucester, VA
Posts: 298
Have you contacted your local Rockwell distributor. They could advise if the files you have are valid backups. They also could advise on local integrators that you could contact to assist.
  Reply With Quote
Old September 20th, 2023, 02:47 PM   #3
mylespetro
Member
Canada

mylespetro is offline
 
mylespetro's Avatar
 
Join Date: Dec 2015
Location: NS
Posts: 737
The action of re-uploading (actually called downloading in this case but I'm not going to open that can of worms lol) the program to the PLC is simple in and of itself, but knowing whether or not the file is valid and/or if there would have been changes made since that file was created is the tricky part. In addition to that, the software licenses are very expensive, so it would likely be cheaper to have a system integrator check it out and download the program to the PLC as glenncovington mentioned. Might be worth a google search for system integrators or automation companies in your area.
  Reply With Quote
Old September 20th, 2023, 03:06 PM   #4
plvlce
Lifetime Supporting Member
United States

plvlce is offline
 
Join Date: May 2017
Location: Michigan
Posts: 967
If you have an up-to-date offline version of the file (which would indeed be an ACD extension), then putting the file back on the PLC is fairly straightforward... as long as you have the software.

The software license is, as mylespetro noted, quite expensive. Check on the PC in case you have it -- the name you are looking for is 'RSLogix 5000'.

If you don't have the software, it's likely to be cheaper to pay an integrator to come out and dump the program back in for you.

If you do have the software and program, the next issue is connecting. You can connect directly to the processor with either a serial cable or via USB, but depending on how the system is set up you may also be able to connect via Ethernet.
  Reply With Quote
Old September 20th, 2023, 03:19 PM   #5
Shimmy
Member
United States

Shimmy is offline
 
Join Date: Sep 2023
Location: USA
Posts: 4
Thank you Glenn. Fellow Virginia resident I'm in Roanoke. I reached out to EEC and they gave me the number for their PLC specialist.

I do have the ACD file and i do have the RS Logix 5000 on the local PC. I had a systems tech friend help me locate them both and we actually had it open and could have done the download but i was unsure and wanted a second set of eyes before i made a serious error. The ACD file has remained unchanged since 2008 when the press was constructed so i know it has not been changed as i was the one to have it put in in 08". I had figured whomever built the system left back ups for us future people and i guess i was right.
  Reply With Quote
Old September 20th, 2023, 03:22 PM   #6
mylespetro
Member
Canada

mylespetro is offline
 
mylespetro's Avatar
 
Join Date: Dec 2015
Location: NS
Posts: 737
Quote:
Originally Posted by Shimmy View Post
Thank you Glenn. Fellow Virginia resident I'm in Roanoke. I reached out to EEC and they gave me the number for their PLC specialist.

I do have the ACD file and i do have the RS Logix 5000 on the local PC. I had a systems tech friend help me locate them both and we actually had it open and could have done the download but i was unsure and wanted a second set of eyes before i made a serious error.
Sounds smart to me, I think you might be up a creek regarding any changes that may have been made over the years, but since you own the machine you'd have a good idea whether or not anyone's ever made any program changes. Better to have the program you have than none at all.
  Reply With Quote
Old September 20th, 2023, 03:25 PM   #7
Shimmy
Member
United States

Shimmy is offline
 
Join Date: Sep 2023
Location: USA
Posts: 4
As luck would have it the unit has never been connected to the Ethernet the entire time i have owned it. So I am positive there have been zero updates.
  Reply With Quote
Old September 23rd, 2023, 03:31 PM   #8
Shimmy
Member
United States

Shimmy is offline
 
Join Date: Sep 2023
Location: USA
Posts: 4
I was able to resolve my issues with help from a local specialist. Guy came buy on his own dime and time and got my issue resolved immediately. I appreciate the assistance you all have offered.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
2D and 3D array in Studio 5000 prakasha LIVE PLC Questions And Answers 8 December 18th, 2022 06:53 AM
ControlLogix to read in Serial Data over RS232 blanchsb1 LIVE PLC Questions And Answers 19 March 2nd, 2021 01:36 PM
AnyBus adapter and ControlLogix (data mis-alignment) phuz LIVE PLC Questions And Answers 6 January 9th, 2016 11:32 AM
Getting data from a check-weigher (ASCII string) into a ControlLogix phuz LIVE PLC Questions And Answers 8 January 4th, 2016 05:02 PM
MPI comunication Manuel Raposo LIVE PLC Questions And Answers 22 July 16th, 2007 08:24 AM


All times are GMT -4. The time now is 11:42 AM.


.