SLC 5/05 1747-L551C ethernet communications to ABB VFD
Hello, I've got a project where I need to get information from two ABB ACS880 VFDs onto the plant operator's screen (or alternatively, onto panelview HMI). I've been reading through the ABB and Rockwell documentation, and I think I've come to the conclusion that the SLC doesn't support the communication that I need. I came across this note in the ABB reference: "NOTE! RSLogix 500 and the PLC processor must support Class 3 messaging." I can't find anything that specifies which class of messaging the SLC 5/05 supports, though the EEM instruction has a field which allows you to specify a class (are they referring to the same classes?: "Class (hex)/(dec) - Possible Classes are 0 to FFFF (hex). See Volume 1 of the CIP Common Specification for the list of defined Classes." I haven't been able to find the CIP Common Specification on Rockwell's library.
Plan B is to bridge the SLC and ControlLogix networks (currently separate) so I can use the ControlLogix PLC's to communicate with the VFD's, though that goes through a wireless bridge which also handles a bunch of other data, so I have bandwidth concerns. Plan C is to try using Ignition's 3rd party Ethernet driver but I think that route would involve a LOT of low level ethernet programming, something I don't think the customer wants to pay me to learn. Has anyone done something similar? Any suggestions? Anything need clarifying or expanding? |
![]() |
![]() |
#2 |
Member
|
I'm not exactly sure if this is conclusive for the SLC, but I have done communication between a MicroLogix 1400 and ABB drives using MSG instructions with no issue. From what I understand, the Micro1400 and SLC are very similar in architecture, but there could very well be a difference in how they handle messaging or Ethernet comms, so I'll defer to some of the people on here who know a bit more of the low-level differences. If it is possible, the ABB website actually had some great example programming (in both .RSS and PDF forms) for the communications. If you get to that point, I can even provide my programming to you to use as a reference.
One caveat was that in my application, the drive had a FENA-21 option module installed, which if I recall correctly is just a separate Ethernet/IP adapter. Last edited by mylespetro; September 12th, 2023 at 04:48 PM. |
![]() |
![]() |
#3 |
Lifetime Supporting Member
![]() ![]() Join Date: Feb 2011
Location: BC, Canuckistan
Posts: 340
|
myles, I do have those references from ABB, that's where the warning about class 3 communications comes from. The SLC MSG instruction does not use MG files, the MicroLogix do. The MSG instruction in SLC looks different than the MicroLogix instruction on the setup screen.
|
![]() |
![]() |
#4 |
Member
![]() ![]() Join Date: Apr 2016
Location: From Canada - Living in Bulgaria
Posts: 2,003
|
How about Plan D: upgrade the SLC 5/05 to a CompactLogix or ControlLogix CPU? That would require changing the driver and tags of the HMI(s) communicating to the SLC as well though. You can use a 1747-AENTR to replace the CPU and keep the existing SLC I/O.
__________________
Automation Programmer PLC / HMI / SCADA / SQL New Systems, Modifications System Upgrades & Conversions Siemens EPROM & EEPROM Service ------------------------ Visit: contrologica.com Email: info@contrologica.com |
![]() |
![]() |
#5 | |
Lifetime Supporting Member
![]() ![]() Join Date: Feb 2011
Location: BC, Canuckistan
Posts: 340
|
Quote:
Looking more and more like going with plan B. |
|
![]() |
![]() |
#6 |
Member
![]() ![]() Join Date: Dec 2010
Location: Harrisonburg, VA
Posts: 828
|
I'm not 100% sure it refers to the same thing, but I found this article that says Class 1 messaging is the implicit messaging you'd get by adding a module to the IO tree of a Logix 5000 PLC while class 3 is explicit messaging using a MSG instruction.
https://www.rtautomation.com/rtas-bl...ss-complexity/ If that's what ABB is talking about, then you should be able to message with a SLC 5/05. Here's a tech note (Access level: TechConnect) that seems to say the same thing: https://rockwellautomation.custhelp....1277/loc/en_US |
![]() |
![]() |
#7 |
Lifetime Supporting Member + Moderator
|
Do you expect to perform start/stop/speed control on those VFDs from the SLC-5/05, or just read status and diagnostic data ?
Which exact EtherNet/IP interface module do the ACS880 drives use ? ABB has had EtherNet/IP modules for years but it's easy to get confused between the various F-series, R-series, and N-series modules. If your SLC-5/05 supports EEM instructions, you should be able to read and write ABB drive parameters using their Drive Parameter Object, class 0x90. |
![]() |
![]() |
#8 |
Lifetime Supporting Member
![]() ![]() Join Date: Feb 2011
Location: BC, Canuckistan
Posts: 340
|
From the SLC instruction manual: "Ethernet/IP Explicit Message instruction for the SLC 5/05 processor (requires series C, FRN 10 or higher OS firmware)." This seems to support your information, joseph.
|
![]() |
![]() |
#9 | |
Lifetime Supporting Member
![]() ![]() Join Date: Feb 2011
Location: BC, Canuckistan
Posts: 340
|
Quote:
The Drives use FENA-21 ethernet modules. Where did you find that class object number? I haven't found anything that details the classes yet. |
|
![]() |
![]() |
#10 |
Lifetime Supporting Member + Moderator
|
I'm working from the User Manual that covers the FENA-01, -11, -21 modules:
https://library.e.abb.com/public/d6a...21_UM_E_A4.pdf The Drive Parameter Object (Class 0x90) is explained starting on Page 239, in Section E. You will need to use the EEM instruction in the SLC-5/05. ABB doesn't emulate SLC-500 data tables the way Rockwell drives do. ABB uses "XX.y" parameter numbering, where XX is the Parameter Group, and the ".y" value is the Parameter. They implement that in their CIP object by making XX = Parameter Group = Instance .y = Parameter Number = Attribute. So to read the Output Frequency (parameter 01.06) of an ACS800, you would use Class 0x90, Instance 0x01, Attribute 0x06. There may be other ways to read a group of data (an Assembly) with a single message, but I am not (yet) familiar with it. |
![]() |
![]() |
#11 | |
Lifetime Supporting Member
![]() ![]() Join Date: Feb 2011
Location: BC, Canuckistan
Posts: 340
|
Quote:
|
|
![]() |
![]() |
#12 |
Lifetime Supporting Member
![]() ![]() Join Date: Feb 2011
Location: BC, Canuckistan
Posts: 340
|
58 words for each EEM instruction, and it looks like a separate EEM for every word (parameter value) that I want to read. So if I want to get 5 parameters, I have to use 3000 words of memory. Nuts.
|
![]() |
![]() |
#13 |
Lifetime Supporting Member
![]() ![]() Join Date: May 2017
Location: Michigan
Posts: 967
|
|
![]() |
![]() |
#14 |
Lifetime Supporting Member
![]() ![]() Join Date: Feb 2011
Location: BC, Canuckistan
Posts: 340
|
|
![]() |
![]() |
#15 |
Lifetime Supporting Member + Moderator
|
The SLC really is fairly efficient on memory use, but yeah, the data that configures a message instruction on Ethernet is relatively bulky compared to a small payload.
Take a look at what the FENA manual calls a "Transparent 32 with two assembly plus drive parameters" object. That might give you the ability to read the drive status plus a block of assorted parameters all at once, with a single EEM message instruction. |
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
SLC 5/05 and printer data (Basic Module to Ethernet) | Skidood | LIVE PLC Questions And Answers | 4 | October 12th, 2016 06:45 PM |
Replacing a VFD... DeviceNet Steps to match new/old controls (SLC 5/05) | AutomationTechBrian | LIVE PLC Questions And Answers | 7 | October 10th, 2013 10:06 PM |
SLC 5/05 Ethernet | mwftech | LIVE PLC Questions And Answers | 16 | August 15th, 2013 11:31 PM |
AB SLC 5/05 serial and ethernet connections | Cleland03 | LIVE PLC Questions And Answers | 10 | March 12th, 2011 10:28 PM |
SLC 5/05 Ethernet Connections | OkiePC | LIVE PLC Questions And Answers | 8 | February 15th, 2010 03:52 PM |