Pencil analoug out from PLC to another PLC input

hi guys, i need 2 diffirent brands to report to each other

the first is a AB Micro850 with 2080-OF2 for 4-20Ma output
the second is Clickplc input 4-20Ma

the old AB needs to report its levels to the new ClickPLC
due to distance 4-20ma is the best option as its only 1 level sensor reading

now wiring for the AB is common and C0 Terminal

does the AB output its own Power source from the AB PLC or do i still need to get 24V dc to the terminals ?
and which would be which ?
i have tried 24V dc to Common - and out from C0 to the new PLC - but that shorts the 24Vdc Power supply

the Recieving PLC is 0V Common and 24V dc + in from the transmitting 4-20ma device

how do i wire the outputs from the AB to the new PLC
  Reply With Quote
Old September 24th, 2023, 06:57 AM   #2
cardosocea
Member
United Kingdom

cardosocea is offline
 
Join Date: Nov 2016
Location: Fields of corn
Posts: 2,562
Quote:
Originally Posted by juddge View Post
does the AB output its own Power source from the AB PLC or do i still need to get 24V dc to the terminals ?
and which would be which ?

when in doubt, I usually take a multimeter and measure if the input channel is giving out voltage. Have you tried that on both ends? Rockwell's manuals tend to be really good at wiring examples for what their IO can do.


Page 10 of this manual has the two possibilities. The question is what is the other PLC expecting.



https://www.routeco.com/en-gb/resour...anual_2080-OF2


Also, because of the distance, the question is somewhat moot. I'd put in a galvanic isolator in the middle just to ensure I don't get reference issues.
  Reply With Quote
Old September 24th, 2023, 09:53 AM   #3
widelto
Member
Colombia

widelto is offline
 
widelto's Avatar
 
Join Date: Jul 2005
Location: Barranquilla, Colombia
Posts: 3,369
I would use an isolator in the middle just for the sake.
__________________
My two cents.
  Reply With Quote
Old September 24th, 2023, 06:27 PM   #4
juddge
Lifetime Supporting Member
Australia

juddge is offline
 
Join Date: Oct 2021
Location: Penrith NSW
Posts: 21
Thanks for the replies
appears the AB has its voltage already, and the Click needs the voltage seperate .

so i may need an isoalter in between them

any recomendations for devices to use as in isoalter between the two ?
  Reply With Quote
Old September 24th, 2023, 10:47 PM   #5
I_Automation
Lifetime Supporting Member
United States

I_Automation is offline
 
I_Automation's Avatar
 
Join Date: Jun 2020
Location: Detroit, Michigan USA
Posts: 1,519
I have a customer with an electroplating line that uses 90 signal conditioners, and they shopped around a lot for the most economical as they seemed to be replacing at least 1 every week.


They introduced me to PR Electronics that they started using for this and all other signal conditioner needs. Their universal transmitter takes mA, VDC, thermocouples, RTD's, potentiometer's and more inputs and has programmable outputs with programmable ranges.


They are very competitive priced and I use them.
__________________
ivanovaautomation.com


Some Jobs Are Best Started With A Sawzall And A Dumpster On Castors
  Reply With Quote
Old September 25th, 2023, 09:29 AM   #6
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 8,170
I have done it before.... not a 800 to Click but I went from a S5 to a SLC and it worked perfect, if you have the time (I did not) I would use a signal conditioner AD sells them

https://www.automationdirect.com/adc...l_conditioners
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, MicroLogix, ControlLogix, Siemens, Allen Bradley and more...OEM and aftermarket supplies... Aftermarket 1784-U2DHP Allen Bradley USB to DH+, new USB to 485 modbus
  Reply With Quote
Old September 25th, 2023, 10:08 AM   #7
joseph_e2
Member
United States

joseph_e2 is offline
 
Join Date: Dec 2010
Location: Harrisonburg, VA
Posts: 828
You mentioned that the 4-20mA is better due to the distance between the PLCs. Are they (or can they be) on the same network? I bet Automation Direct would help you set up a messaging scheme between them so you could get the data across without analog signals at all.
  Reply With Quote
Old September 25th, 2023, 10:11 AM   #8
Rob...
Lifetime Supporting Member
United Kingdom

Rob... is offline
 
Join Date: Jul 2016
Location: Manchester
Posts: 460
Quote:
Originally Posted by I_Automation View Post
I have a customer with an electroplating line that uses 90 signal conditioners, and they shopped around a lot for the most economical as they seemed to be replacing at least 1 every week.


They introduced me to PR Electronics that they started using for this and all other signal conditioner needs. Their universal transmitter takes mA, VDC, thermocouples, RTD's, potentiometer's and more inputs and has programmable outputs with programmable ranges.


They are very competitive priced and I use them.
Agreed, I've used PR electronics numerous times, all work exceptionally.

Quite handy as a lot of them can be gotten with a basic digital output screen, that shows the raw values being received/output. Helps with troubleshooting.
__________________
  Reply With Quote
Old September 25th, 2023, 11:25 AM   #9
mylespetro
Member
Canada

mylespetro is offline
 
mylespetro's Avatar
 
Join Date: Dec 2015
Location: NS
Posts: 737
Quote:
Originally Posted by Rob... View Post
Agreed, I've used PR electronics numerous times, all work exceptionally.

Quite handy as a lot of them can be gotten with a basic digital output screen, that shows the raw values being received/output. Helps with troubleshooting.
I would also recommend Acromag isolators without hesitation. Not sure how available they are in Australia, but I find them very easy to configure and haven't had one fail on me yet.
  Reply With Quote
Old September 26th, 2023, 05:30 AM   #10
mikeexplorer
Supporting Member
United States

mikeexplorer is offline
 
Join Date: Nov 2018
Location: Scranton,PA
Posts: 155
I have used this one and it works well


https://www.automationdirect.com/adc...er_input/fc-11
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
RSLogix 500 - I/O mapping question toads LIVE PLC Questions And Answers 8 September 25th, 2019 01:40 PM
Phoenix Contact PLC Analogue input card Jayden LIVE PLC Questions And Answers 1 July 25th, 2016 12:03 PM
I want to run PLC on bench with an incorrect input card realolman LIVE PLC Questions And Answers 11 February 26th, 2014 03:34 PM
Proximity Switch to PLC Input narcilla LIVE PLC Questions And Answers 0 March 19th, 2010 04:53 PM
Real World Problem Vietnam Bob LIVE PLC Questions And Answers 8 November 23rd, 2002 04:03 PM


All times are GMT -4. The time now is 12:32 PM.


.