From 1769 sm2 Module To Honeywell Temprature Controller Via Modbus Communication

karthikolive

Member
Join Date
Oct 2010
Location
*******
Posts
12
Dear all!
I am trying to Communicate with one temperature controller(Honeywell DC1040) using Miglogix1500&1769sm2 module via Modbus Communication(Write Single Coil Value).Any one Knows Help me.If possible send sample program.
 
I doubt the Honeywell DC1040 talks Modbus.
The instruction manual for the DC1000 series here
http://hpsweb.honeywell.com/NR/rdonlyres/8852A2AF-F058-4569-921F-18BBC8681A5C/33211/515225113.pdf
does not mention the word Modbus.

The DC 1000 series spec sheet here:
http://hpsweb.honeywell.com/NR/rdonlyres/DD9BC3B0-FF6A-4C10-BC52-9307FD8D44B3/33020/51520333.pdf
mentions an ASCII protocol, but not the Modbus protocol.

"Communications
RS232 or RS485 ASCII protocol is optionally available. Up to 30 DC1000 Controllers can be connected to a single host computer. The host computer can change the SP, monitor the PV, the output or change the configuration of the unit."


The Modbus RTU manual 51-52-25-66 that covers Honeywell controllers, recorders and actuators has a list of device manuals on page 1 (paper), pg 7 pdf, where the DC1000 series is conspicuously absent from the list.
http://hpsweb.honeywell.com/Culture...tion/controllers/DC1000/Manuals/Documents.htm

It appears that the Honeywell web site does not have an ASCII communications manual for the DC1000.

Good Luck talking Modbus to an undocumented device.
 

Similar Topics

Hello! I have a one problem with 1769-SM2 module... I use PLC 1768-L43 and modbus module 1769-SM2. There are 4 devices in modbus net: CH1 - two...
Replies
27
Views
9,254
Can we use 1769 SM2 module for communicating energy meters on modbus.
Replies
2
Views
3,370
Hi Project's PLC is a 1769-L36ERM used with a Siemens LME73 Flame controller. I have to establish communication between these devices thru a...
Replies
2
Views
1,577
So I have a system that is running on DeviceNet. We have been having nothing but problems with it for the last 3 years. I am trying to switch...
Replies
2
Views
1,272
Hello everyone. I'm trying to communicate a Controllogix L36ERM with a 1769-SM2 Modbus module to a Schneider-electric Altivar 312 Modbus motor...
Replies
7
Views
2,469
Back
Top Bottom