cp 343-1 lean hardware config in software

sibi05.aat

Member
Join Date
Sep 2008
Location
bangalore
Posts
25
hi,
I m using the CPU314 (6ES7 314-1AG13-0AB0) and the cp card is CP-343-1 LEAN (6GK7 343-1CX00-0XE0).In this I m not using any I/O module near the CPU.
While hardware configuration I can’t able to configure the Ethernet connection between the cp card and the interface module IM 151(6ES7 151-1AA04-0AB0).
plz let me know how to configure the ethernet connection in the software part.
 
Hi.

1st. The CP343-1 LEAN can be used as a Profinet "device" (i.e. slave) not as a Profinet "controller" (i.e. master). So it cannot be setup to control an IM151-3 for example.

2nd. The IM151-1 is for Profibus DP, not ethernet.

The 314 CPU does not have a DP port, and the CP343-1 LEAN is for ethernet, besides that it cannot be a Profinet Controller. So with your present hardware you cannot connect an IM151-1.

I think the most obvious solution (out of several) is to use a CP342-5. This can be a Profibus DP master for the IM151-1 DP slave.
 
sibi05.at said:
is there any way to configure the cpu 314 with IM-151.
JesperMP said:
I think the most obvious solution (out of several) is to use a CP342-5. This can be a Profibus DP master for the IM151-1 DP slave.

sibi05.at said:
and could u tell me which CP-CARD can i use for industrial ethernet.
The CP343-1 LEAN is already OK for "Industrial Ethernet" (aka IE).
For the S7-300 to be a ProfiNet Controller, you need a CP343-1 such as the 6GK7343-1EX30-0XE0. However, you cannot connect the Profibus IM151-1 to this ProfiNet controller !
 

Similar Topics

Hi all, I'm trying to fit a CP343-1 Lean card (v3.0 6GK7 343-1CX10-0XE0) on to an existing rack that has a CPU318-2 (6ES7 318-2AJ00-0AB0) in...
Replies
2
Views
4,688
Hi , Looking for some help. We have a 343-1 PN Lean Card & 315-2DP connected to an external system collecting data. After a recent shutdown...
Replies
0
Views
63
Hello to All, Recently I install a CP343-1 Lean to communicate with a CPU 314 IFM, however I can't go online when I'm connected via CP343-1 Lean...
Replies
4
Views
1,666
I can not see the CPU s7-300 i only see the cp343 as photo the interface is through tcp/ip how can I upload the station via the cp343 module ???
Replies
2
Views
1,002
Hi all, I have a CPU315-2 PN/DP with a CP card, which is CP343-1 Lean. I have a PI server and am trying to connect to the Lean card. I can ping...
Replies
9
Views
3,703
Back
Top Bottom