Siemens S7 PLC Profibus error

mvannantn

Member
Join Date
Jan 2003
Location
bangalore
Posts
32
All the siemens drives are through profibus.Due to internal problem one of the drive was taken out from the network.Now i needs to run without this drive.But the OP is giving fault alarm that the profibus drive error of the removed drive.

its very urgent to run the machine. some one give your idea to set right our machine for production


Manivannan
 
Hi

If there is an alarm on the OP, then this means that there is programmed something I think.

Else, try this:

check the termination resistor, if it's the last drive on the network, then the previous one should be terminated, and else it's no prob.

Check Module Information if the CPU is in stop, look for wich OB's are asked. If OB87, then make OB87 and download it.


If you use feedbacksignals of the drive in your program to prevent to start the machine, then you'll need to make program changes...



mvannantn said:
All the siemens drives are through profibus.Due to internal problem one of the drive was taken out from the network.Now i needs to run without this drive.But the OP is giving fault alarm that the profibus drive error of the removed drive.

its very urgent to run the machine. some one give your idea to set right our machine for production


Manivannan
 
Hello manivannan.

What error is it that the OP displays ?
Are there no mechanical reasons why the machine cannot run without the drive ?

Anyway, if there is an interlock in the program that requires the drive to be present, then you should contact the original programmer. It is faster than trying to dissect a program made by someone else.
 
If the drive is being accessed using load/transfer instructions to the relevant PIW/PQW address you will have prevent these instructions from executing (by jumping around them for example).

Similarly, if SFC14/15 is being used to transfer data to/from the the drive and the error status being returned from the sfc is causing the error, you will need to jump around the processing for the missing drive.

(NB: I am assuming this is an S7-300/400 system)
 
OB's

Loading the Error OB's helps too I think


L D[AR2 said:
If the drive is being accessed using load/transfer instructions to the relevant PIW/PQW address you will have prevent these instructions from executing (by jumping around them for example).

Similarly, if SFC14/15 is being used to transfer data to/from the the drive and the error status being returned from the sfc is causing the error, you will need to jump around the processing for the missing drive.

(NB: I am assuming this is an S7-300/400 system)
 
Not unless you understand the full ramifications. For example if another drive falls off the bus then the machine will (try to) keep going causing possible damage.
 

Similar Topics

Kindly, we are trying to go online on an S7-300 plc, with profibus communication, using a CP5711 adapter. But when we open the Ladder and press...
Replies
0
Views
770
Dear Sir, I have a healthy profibus communication between SIEMENS PLC S7 400 and Allen Bradley drive PF700 using 20-comm-p profibus dp module...
Replies
3
Views
2,790
Dear all, In the past I have used DP/PA Links with Siemens PLCs. As both the Link and the PLC was from the same vendor, ther was no trouble...
Replies
2
Views
3,069
Greetings Can the Profibus network ، Schneider Premium PLC with TSXPBY100 Module was selected as Slave? I'm going SIEMENS PLC (S7-400) as master...
Replies
3
Views
2,335
In plant we use Siemens S7 PLC CPU 319F-3 PN/DP with profibus connected to remote I/Os. Profibus network have profibus nodes. We are getting...
Replies
4
Views
6,981
Back