Rockwell Panelview momentary pushbutton problem

We have a compact logix L32E running RsLogix 5000 v.20, connected to two panelview plus 6 1000 over ethernet.

1) One, possibly both panelviews have started losing the connection to the PLC occasionally, after no problems for months. They are connected through a dumb switch. Cycling power on the control panel has fixed the comm loss. We are trying to figure out what would cause the comm loss.

2) We have noticed that when the panelview loses the comms, some of the momentary pushbutton commands from the panelview staid ON in the PLC. (Not sure if an operator was pressing a button when the comms went off). I tested this later by pressing a button and disconnecting the ethernet from the panelview, and the bit stays ON in the PLC. Searching online reveals that other people solve this problem by periodically unlatching all momentary bits from the panelview in the PLC. I was just wondering if there was a more elegant way to deal with this problem.

I tried to set up the panelview in the I/O Config and the PLC can see it, but I get errors because the assembly instance size is incorrect, and I can’t seem to find the correct one. If I could get it to talk is it possible to see a panelview comm fault and then clear the data in the PLC?
Thanks.
  Reply With Quote
Old June 24th, 2019, 04:44 PM   #2
kamenges
Member
United States

kamenges is offline
 
kamenges's Avatar
 
Join Date: Nov 2002
Location: Brillion, WI
Posts: 4,276
The Panelview Plus 6 cannot be set up as an I/O connection. The connection is a peer-to-peer connection, similar to connecting your computer to the plc. The only way I am aware of to reset bits set from a Panelview Plus is to unlatch them in the program. Not much good for jogs, though.

As a side note, the Panelview 5000 can be set up as an I/O connection to a plc. That doesn't do you much good but that is where you would need to go for an Ethernet/IP connected Panelview.

Keith
  Reply With Quote
Old June 24th, 2019, 04:57 PM   #3
martinzstl
Member
United States

martinzstl is offline
 
Join Date: Mar 2019
Location: STL
Posts: 3
Ok thanks.

I set up a five second timer to reset the panelview bits. This allows the operator to jog for few seconds before they have to press the button again. Annoying, but better than something running continuously with no control.

I just wish I knew why the panelview is dropping comms. Normally they just work all the time. It's not a complex setup. Panelview, ethernet cable, dumb switch, ethernet cable, PLC. I wonder if overheating can cause the panelview to do weird things.

We do also have a Network Address Translator router to get the plant network to talk to the PLC and HMI. Maybe that can cause problems.
  Reply With Quote
Old June 24th, 2019, 05:22 PM   #4
janner_10
Lifetime Supporting Member
United Kingdom

janner_10 is offline
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 1,300
Have you replaced the Ethernet cable first between the two units?

Do the simple things first.
  Reply With Quote
Old June 24th, 2019, 06:04 PM   #5
mellis
Member
United States

mellis is offline
 
Join Date: Nov 2004
Location: Cincinnati, Ohio
Posts: 828
Rather then use a timer to unlatch the bits, I prefer to unconditionally unlatch them right after the logic that uses them. It's simpler, less instructions and tags. This works fine for start/stop pushbuttons.

In my mind, it's always important to deal with the "stuck on" condition.
  Reply With Quote
Old June 25th, 2019, 06:12 AM   #6
Geoff White
Member
Australia

Geoff White is offline
 
Join Date: Oct 2005
Location: Brisbane
Posts: 446
Quote:
rather then use a timer to unlatch the bits, i prefer to unconditionally unlatch them right after the logic that uses them. It's simpler, less instructions and tags. This works fine for start/stop pushbuttons.

In my mind, it's always important to deal with the "stuck on" condition.
+1
  Reply With Quote
Old June 25th, 2019, 06:25 AM   #7
Mad_Poet
Member
United States

Mad_Poet is offline
 
Join Date: Feb 2017
Location: Virginia
Posts: 375
Martin > I just wish I knew why the panelview is dropping comms.
Martin > We do also have a Network Address Translator router to get the plant network to talk to the PLC and HMI


Any chance something on the rest of the network has the same IP
as either the panelviews or the PLC?
Poet.
  Reply With Quote
Old June 25th, 2019, 08:01 AM   #8
Ken Moore
Lifetime Supporting Member
United States

Ken Moore is offline
 
Ken Moore's Avatar
 
Join Date: May 2004
Location: North, West, South Carolina
Posts: 3,317
I have run into similar issues, where the number of connections in the PLC is exceeded. For some reason, Ethernet connections do not get closed properly and overtime you end up with a bunch of connections open, the PLC runs out of connections and will not communicate with anything. Cycling power to the PLC, closes all the connections and you are okay for a period of time. When the panels lose comms, can you go online with a laptop?
__________________
Certified Siemens Functional Safety Professional,
ID: SFSP17010238
NRA Benefactor
  Reply With Quote
Old June 25th, 2019, 09:50 AM   #9
rdrast
Lifetime Supporting Member
United States

rdrast is offline
 
rdrast's Avatar
 
Join Date: Apr 2003
Location: South Carolina Lowcountry
Posts: 5,537
Quote:
Originally Posted by mellis View Post
Rather then use a timer to unlatch the bits, I prefer to unconditionally unlatch them right after the logic that uses them. It's simpler, less instructions and tags. This works fine for start/stop pushbuttons.

In my mind, it's always important to deal with the "stuck on" condition.

That works for many things, but not Jog type functions.
__________________

  Reply With Quote
Old June 25th, 2019, 10:36 AM   #10
kamenges
Member
United States

kamenges is offline
 
kamenges's Avatar
 
Join Date: Nov 2002
Location: Brillion, WI
Posts: 4,276
I'm fairly certain the L32E has a web page. You might want to open that when this happens and look at the network diagnostics section. That might give you some clues as to what is happening. Even if all the Ethernet/IP connections are chewed up I THINK the web page will still serve up pages.

Keith
  Reply With Quote
Old June 25th, 2019, 10:56 AM   #11
martinzstl
Member
United States

martinzstl is offline
 
Join Date: Mar 2019
Location: STL
Posts: 3
"Any chance something on the rest of the network has the same IP
as either the panelviews or the PLC?"

-The plant network has a different IP range. The local has the standard 192.168.x.x


"Rather then use a timer to unlatch the bits, I prefer to unconditionally unlatch them right after the logic that uses them. It's simpler, less instructions and tags. This works fine for start/stop pushbuttons."

-Unfortunately, most of my HMI buttons are jog buttons that need to stay on for at least a few seconds.


"I have run into similar issues, where the number of connections in the PLC is exceeded. For some reason, Ethernet connections do not get closed properly and overtime you end up with a bunch of connections open, the PLC runs out of connections and will not communicate with anything."

-If it happens again we will try to go online. Also maybe cycle power just to the PLC and then see if the panelview reconnects.

-Thanks for all these suggestions. We have two other systems with a similar setup and they don't seem to have this problem as far as I know. Maybe it is just a flaky ethernet cable on this system. We will have to monitor it for now and see if it keeps dropping comms.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
STEP 7 and RSLogix5000 DamianInRochester LIVE PLC Questions And Answers 69 September 17th, 2016 02:14 AM
Panelview Plus Firmware Upgrade Problem woodward_uk LIVE PLC Questions And Answers 4 September 2nd, 2015 05:31 AM
panelview 700 real bad problem jimcav LIVE PLC Questions And Answers 3 February 15th, 2011 12:03 AM
Factory Talk View Normally Closed Pushbutton Problem steven_s_54 LIVE PLC Questions And Answers 6 May 6th, 2010 05:12 PM
Panelview plus 1000 compact download problem Matthewn LIVE PLC Questions And Answers 10 March 22nd, 2010 10:35 PM


All times are GMT -4. The time now is 11:31 PM.


.