Converting Temperature PID from Siemens Step 7 to Portal

Barry Kirk

Lifetime Supporting Member
Join Date
Mar 2007
Location
York, PA
Posts
61
I'm in the process of converting over a temperature loop from Step 7 to Portal.

The old Step 7 program uses FB58 TCONT_CP for the PID block.

In the old program the manipulated value could range from -100% to +100%. If the value of the manipulated value was over 0, than I ran the Q_Pulse output straight into the output to drive a solid state relay that fired my heater element.

If the value of the manipulated value was less than zero, than I sent it to some code that fired a cooling fan.

With Portal, the TCONT_CP claims to be only useful for pure heating or pure cooling loops and the manipulated value lower limit seems to have a minimum value of zero.

Are there any blocks for heating/cooling loops in Portal, or is there any way to get around the limitation of a manipulated value lower limit minimum value of zero?
 

Similar Topics

im using DVP-04pts and here is the download link to see its output...
Replies
5
Views
1,866
Hello everyone, can anyone help me with covert the STL code to ladder. Iam using plc s71200. A %DB1.DBX33.7 // angel of vaccum...
Replies
2
Views
208
Hello PLCs Forum, I am in a bit of a pickle and was hoping someone could offer me some help. I have a .rss file and just need to see the ladder...
Replies
2
Views
121
Hello nice to meet you, im new in here, I'm currently trying to convert code written in STL for a S7-400 to SCL for an S7-1500, because when i run...
Replies
5
Views
317
Hello, did anybody know, if there exist an converting cable like the1492-CM1746-M01 (for an 1746-IB16 to an 5069-IB16), for an 1746-HSCE to an...
Replies
3
Views
389
Back
Top Bottom