Turck BL20 analog and Siemens S7

JRW

Member
Join Date
Jun 2002
Location
South Carolina
Posts
2,300
When using Turck BL20 analog and Siemens S7 can someone tell me if the scaling in S7 is still 0-27648 (for 0-10vdc/4-20ma) or is it something else?

I have the manual but I dont see those details,

THANKS
 
You have not stated the model of the PLC or analogue card it will depend on if it is 12 or 16 bit conversion 16 bit is 27648 I believe
 