Control logix Plc Time Sync

The last reply was 2020. Oh btw, it seems AB discontinued 1756-TIME all together.

So the only option to sync directly to a real good PTP source is buy a GPS with PTP functionality like SEL 2488.
 
If there is one on the network a Stratix 5700 or 5400 can read a NPT server and be the time Grandmaster.
 
A SCADA Script should be able to read the PC (Server) time and then Write it to Tags in the PLC once every couple of hours, where you can update the wall clock. The PLC can then be a PTP time server for the network. This saves having to have RSLinx and Clock Sync Tool if you already have an OPC interface to the PLC
 
We just implemented the socket solution and that worked fairly well, not straightforward, but it works. I don't have tech connect so I can't search for it. But if you do:

RSLogix 5000 : AOI example for using sockets to read time from NTP or SNTP server

ID: QA49644 | Access Levels: TechConnect
 

Similar Topics

Hi I want to press a button on the HMI screen and write to a bit within an Integer within a control logix PLC. The iFix version is 5.5 and using...
Replies
3
Views
2,390
Can an HMI access the control logix plc tag's Description? It's relatively new that the PLC stores the PLC tags descriptors in it's own plc...
Replies
1
Views
1,300
Dear All. I need comm between Compactlogix/Controllogix with PNOZ m1p ETH. What we need the communication option? or can be connect direct? many...
Replies
0
Views
1,174
Dear All, I would liket to ask for your help. I have a L73S PLC which communicates with a Soft Siemens PLC by MSG. (I already got the system...
Replies
2
Views
1,359
Is there a way to upload all of the tags with their current values from the PLC? I am using Studio 5000 version 31.11. We need a snapshot of the...
Replies
12
Views
4,833
Back
Top Bottom