Old August 9th, 2021, 01:10 AM   #1
Kman13
Member
Germany

Kman13 is offline
 
Join Date: Aug 2021
Location: Germany
Posts: 3
PanelviewPlus 1000 Tag Update rate

Hello to the community,

I am new to Rockwell and I have a small problem with a PvP1000(2711P).

Some buttons in the same screen are not refreshing with the same rate as some others. For example, I press a Button AUTO, the machine is running in AUTO but the button turns green after 20sec. That can happen with more than one buttons. If I restart the Panel, maybe the AUTO button will work fine and now another button will have the same problem.

At this point I want to mention that in Display settings the Maximum Tag Update Rate is set to 0,25 sec.

Do you have any ideas what could cause this?

Thank you in advance.


Firmware versions:

OS :02.57.0.0
ME Station: 10.0.0.290
  Reply With Quote
Old August 9th, 2021, 06:27 AM   #2
gclshortt
Member
Canada

gclshortt is offline
 
gclshortt's Avatar
 
Join Date: Dec 2014
Location: Ontario
Posts: 3,220
http://www.plctalk.net/qanda/showthread.php?t=75982
The above thread may help you out.
Regards,
__________________
Garry
https://www.accautomation.ca
Connect with us on Facebook: facebook.com/accautomation/
  Reply With Quote
Old August 9th, 2021, 08:53 AM   #3
Kman13
Member
Germany

Kman13 is offline
 
Join Date: Aug 2021
Location: Germany
Posts: 3
Quote:
Originally Posted by gclshortt View Post
http://www.plctalk.net/qanda/showthread.php?t=75982
The above thread may help you out.
Regards,
Thank you for your answer but the mentioned post did not really help me. My problem is only the indication of the button's state. When I press the button the bit is setted but the state is not refreshed. If go out of the screen and open it again then it will be updated. Strange is that whenever I restart the Panel, the problem appears to different buttons. So the same button maybe after a new restart will be ok and the problem will be at another.
  Reply With Quote
Old August 9th, 2021, 04:07 PM   #4
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is online now
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 17,254
Welcome to the PLCTalk community !

The PanelView Plus has a reputation for having relatively slow and inflexible screen refreshes: all of the tags on a Display update at the same rate.

But the default of 1 second should be successful. 20 seconds suggests a problem beyond performance.

I recommend test-running the application on a FactoryTalk View development PC so you can see the FactoryTalk Diagnostic Log, or create a Display in your PanelView Plus project that has a diagnostic log object.

My guess is that there is a syntax error somewhere in the project and the tags are being updated in between automatic attempts to optimize tag reads, which can take a long time.
  Reply With Quote
Old August 10th, 2021, 01:36 AM   #5
Kman13
Member
Germany

Kman13 is offline
 
Join Date: Aug 2021
Location: Germany
Posts: 3
Quote:
Originally Posted by Ken Roach View Post
Welcome to the PLCTalk community !

The PanelView Plus has a reputation for having relatively slow and inflexible screen refreshes: all of the tags on a Display update at the same rate.

But the default of 1 second should be successful. 20 seconds suggests a problem beyond performance.

I recommend test-running the application on a FactoryTalk View development PC so you can see the FactoryTalk Diagnostic Log, or create a Display in your PanelView Plus project that has a diagnostic log object.

My guess is that there is a syntax error somewhere in the project and the tags are being updated in between automatic attempts to optimize tag reads, which can take a long time.
Hello Ken,

I deleted all the faulty buttons and I recreated them. Now it seems to work. Something went wrong but I do not know what. Thanks for your answer. I will have it on mind for the future.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Panelview Tag Update Time andy_1983 LIVE PLC Questions And Answers 2 November 4th, 2022 10:38 AM
PanelView Plus 1000 fail to go to specified display in remote display control tag JDFP LIVE PLC Questions And Answers 1 July 8th, 2021 07:51 AM
IntouchWonderware Tag update bayeibrahima LIVE PLC Questions And Answers 0 June 6th, 2013 10:34 AM
OPC Update Rate Sceptre LIVE PLC Questions And Answers 0 February 18th, 2004 02:49 PM
how often should I trigger the PID? Ron Beaufort LIVE PLC Questions And Answers 11 February 22nd, 2003 11:57 AM


All times are GMT -4. The time now is 09:19 AM.


.