PanelviewPlus 1000 Tag Update rate
Hello to the community,
I am new to Rockwell and I have a small problem with a PvP1000(2711P). Some buttons in the same screen are not refreshing with the same rate as some others. For example, I press a Button AUTO, the machine is running in AUTO but the button turns green after 20sec. That can happen with more than one buttons. If I restart the Panel, maybe the AUTO button will work fine and now another button will have the same problem. At this point I want to mention that in Display settings the Maximum Tag Update Rate is set to 0,25 sec. Do you have any ideas what could cause this? Thank you in advance. Firmware versions: OS :02.57.0.0 ME Station: 10.0.0.290 |
![]() |
![]() |
#2 |
Member
|
__________________
Garry https://www.accautomation.ca Connect with us on Facebook: facebook.com/accautomation/ |
![]() |
![]() |
#3 | |
Member
![]() ![]() Join Date: Aug 2021
Location: Germany
Posts: 3
|
Quote:
![]() |
|
![]() |
![]() |
#4 |
Lifetime Supporting Member + Moderator
|
Welcome to the PLCTalk community !
The PanelView Plus has a reputation for having relatively slow and inflexible screen refreshes: all of the tags on a Display update at the same rate. But the default of 1 second should be successful. 20 seconds suggests a problem beyond performance. I recommend test-running the application on a FactoryTalk View development PC so you can see the FactoryTalk Diagnostic Log, or create a Display in your PanelView Plus project that has a diagnostic log object. My guess is that there is a syntax error somewhere in the project and the tags are being updated in between automatic attempts to optimize tag reads, which can take a long time. |
![]() |
![]() |
#5 | |
Member
![]() ![]() Join Date: Aug 2021
Location: Germany
Posts: 3
|
Quote:
I deleted all the faulty buttons and I recreated them. Now it seems to work. Something went wrong but I do not know what. Thanks for your answer. I will have it on mind for the future. |
|
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Panelview Tag Update Time | andy_1983 | LIVE PLC Questions And Answers | 2 | November 4th, 2022 10:38 AM |
PanelView Plus 1000 fail to go to specified display in remote display control tag | JDFP | LIVE PLC Questions And Answers | 1 | July 8th, 2021 07:51 AM |
IntouchWonderware Tag update | bayeibrahima | LIVE PLC Questions And Answers | 0 | June 6th, 2013 10:34 AM |
OPC Update Rate | Sceptre | LIVE PLC Questions And Answers | 0 | February 18th, 2004 02:49 PM |
how often should I trigger the PID? | Ron Beaufort | LIVE PLC Questions And Answers | 11 | February 22nd, 2003 11:57 AM |