It's been a long time since I played with an old PV1000. With the momentary pushbuttons, is there really no way to let you push/hold a button (ie, you can only use the "hold time")
In Panelbuilder32, the Momentary Button Hold Time should be thought of as Minimum Hold Time.
The Write Tag will be written to when the button is pressed, and change back when the button is released or the hold time is reached, whichever comes last. In other words, assume a normally open button writing to a bit, if you keep the button pressed, the tag will stay "1".
Unless it is a jog button where you want to be able to bump it very briefly, I typically set the minimum hold time at 500ms which in most cases is enough time for the communication to occur between the HMI and PLC.
Yeah, OK, this is what I was expecting it to do (like in a PV+), but in the PV1000 (Panelbuilder32), it releases right away and does not stay "pressed" while your finger is on the button. I wonder if it's something with the RIO.
It should wait for the Hold Time or the button to be released before changing to the OFF state even on RIO, but maybe there is an exception I have not run into before. I sure don't miss those fun days of dealing with RIO and multiple block transfers for an HMI.
I ran into an application once where the guy used 1 logical rack for hundreds of tags and use the Page Number to multiplex the data so the PLC mapped the values in and out of one small block of addresses based on the page number. That allowed him to put dozens of servo recipes in the logic and HMI without having to change the hardware.
Such a PITA to debug! There was a spot where the operator could enter a zero for velocity of an axis and the machine would promptly obey sitting there hung up with no errors. I couldn't just go in and edit the entry limits for that tag because it was used for 9 other things that needed to have 0 available as an entry limit. It took me several hours to trace it down to a spot in the PLC where I could limit check it.
If there is another object in the application using that same PLC address that could explain the behavior you're seeing. I looked through the Knowbase and didn't find anything referencing this, but I did find a tech note that said the Hold Time begins when the operator releases the button.
Depending on the situation, you still may want to put a time limit on the jog operation in the PLC code once you get it working.