Quote:
Originally Posted by ASF View Post
Not all drives have safe torque off, if yours doesn't you can disregard.

The drive can be configured to look at Modbus, Digital Inputs, or Both. Make sure it's not set to both.

As per my previous post, Reference 1 Source is the parameter you need to look at for sending a speed reference over modbus. Of course you also need to make sure that Reference 1 is selected, but generally it will be selected by default.
Ah thank you. I have set the drive to listen to both Digital Inputs and Modbus. So it might be that. Can't make changes at the moment but will certainly look at that when the load shedding ends.

For content: South Africa has about 8 hours a day at almost random intervals where our power is cut but the employees of the national power provider because they want additional wages increases... makes working to a schedule very difficult.
  Reply With Quote
Old July 7th, 2022, 07:27 PM   #17
ASF
Lifetime Supporting Member
Australia

ASF is offline
 
Join Date: Jun 2012
Location: Australia
Posts: 3,579
It's likely that's the case. If you're listening to both digital inputs and modbus, you're probably getting a start signal from modbus and a stop signal from the digital inputs (because the stop signal will be a "0=stop, 1=no stop" arrangement, and your stop input is not connected), and a stop input will override a start input. I don't know this for sure as I've not used Danfoss drives extensively, but on other drives I am more familiar with, that's exactly how it works.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
allen bradely 525 drive trouble mavrick LIVE PLC Questions And Answers 16 May 24th, 2019 01:07 PM
Allen Bradley Powerflex 753 Drive Error Nandraj LIVE PLC Questions And Answers 4 October 2nd, 2018 03:14 PM
Looking for a rebuilt Allen Bradley 1336 Impact 250 Hp Drive Rob S. LIVE PLC Questions And Answers 6 April 26th, 2016 06:14 PM
Powerflex 40 drive suddnly stopping while running & there is no alarm on the display sahebanna LIVE PLC Questions And Answers 1 April 2nd, 2012 02:51 AM
Abb Ac Drive rajendrad LIVE PLC Questions And Answers 13 November 5th, 2006 11:18 AM


All times are GMT -4. The time now is 04:30 PM.


.