Im looking to replace a retroreflective Photoeye with a throughbeam or light curtain. The retroreflective eye is causing some issues with reflective tape on boxes so i want to eliminate this problem. 42EF-P2MPB-F4 is the part number for my photoeye. Standard M12 connection running to an allen bradley SIO module, 24vdc PNP sensor. Im just not sure which specs are important when finding a replacement. And if my replacement is a throughbeam sensor, i have questions as to what additional changes would be required. I would then need an additional M12 cable for the extra powered device. And just not sure what that looks like in the logic. If studio would require any changes due to the extra cable, or how would i provide power to that additional device (transmitter/receiver)--- Any info would be greatly appreciated. I am a controls technician but still a little green in my second year.
 
Unless the item is part of the IO tree then the PLC does not care what is connected to a digital Input.
As for wiring the transmitter of a through beam unit will only need power so again the PLC does not know about that.
Just get a supply from where the current Photoeye gets its power from and run it to the transmitter, and run the receiver signal back to the PLC using the existing wires.
 
Im just not sure which specs are important when finding a replacement. And if my replacement is a throughbeam sensor, i have questions as to what additional changes would be required. I would then need an additional M12 cable for the extra powered device. And just not sure what that looks like in the logic. If studio would require any changes due to the extra cable, or how would i provide power to that additional device (transmitter/receiver)

For PNP you should have three connections: power, common and switched output. If it's both NPN and PNP you may have a fourth connection for the NPN output too.
For a throughbeam you would need power to the emitter, but you can just pick this up from the power and common terminals of your receiver.
As Alan said, all the PLC is looking for is 24v coming back to the input card.

We use these: https://www.keyence.com/products/sensor/laser/lr-t/.
Very precise sensing up to 5 meters. NPN, PNP or analog output.

These are good and very robust, but Keyence stuff can be quite expensive. If the analog is needed, it's only available on the 5m model and not the 2m.
 
sometimes you don't need a different sensor, you just need to mount them differently.

for instance, if you are reading reflective tape as part of the retroreflective sensor and it's triggering more than you need to. then consider that you should try to put your current sensor and reflector at an angle to the parts coming by, reflectors for these sensor are built to reflect back anything at the angle it came in at. tape on a box is not, so while you can get a reflection off tape while point at it from a perpendicular angle, you won't get that is most cases when you shoot off to the side.

If you can't just move the sensor and reflector at an angle, then possibly change the height they sit at to avoid the tape as much as possible.

if the sensors just can't be moved, then consider going with a diffuse (depending on the situation), Diffuse sensors don't use a reflector so they can't be tricked halfway through a part passing by unless there is a hole in something, but then it wouldn't matter because a retroreflective would also fail here too (which is why pallet sensing applications usually have sensors aimed at extreme angle where there are no gaps in pallets).


try some physical fixes before swapping to a whole new style sensor, it might work.
 
The retroreflective eye is causing some issues with reflective tape on boxes so i want to eliminate this problem.
A through-beam sensor does sound as if it the simple solution you are looking for.
There are other methods, but if you have the possibility to install a trough-beam, then that is what I would recommend. There are millions of these out there working in environments with reflections, false light sources etc.
 
Yes through beam is definitely the answer, done this many times, we have had some really interesting ones.
Called to some conveyors where they were having problems with intermitent triggering of photocells, seemed weird as the cartons were not reflective but often detected no carton when there was one there, turned out to be a forklift yellow beacon triggering the photocell as it went past.
Had the same thing on some light curtains, took a couple of trips to find out what it was, just happened to notice it occured when a forklift passed the machine, solution some cardboard taped to the guard cage, after all, it was a cardboard box manufacturing company, not sure if they ever replaced it with something a little more aesthetic.
 
I had a similar situation on a reflective photoeye.

A table rose with a stack of circuit boards and interrupted the beam to the reflector, then the machine grabbed the top one and took it off.

The problem was some boards were electroplated after a conductive coating was applied to the inside of the hole - AND the outside edges. On those the sides got plated with very shiny copper.

The photoeye was suddenly reflected of the shiny edge and didn't go dark.

I ended up having to change the machine to a prox above to sense up.

Another problem with photoeyes was the shop was changed from mercury vapor highbay lights to all LED's and the new LED light would trip and hold on any photoeye it shined on.
 
I went with through beam when we started running product in plastic wrap. Since you have the M12 connector simply attach a T splitter to it and a short cable back to new through beam (receiver) and another cable off splitter to the (emitter)
 

Similar Topics

I have a bunch (20+) of Yaskawa GS5 inverters and would like to connect them to our modbus network. Unfortunately, they only have native RS-232...
Replies
6
Views
2,227
Hi , Where i can find Mitsubishi PLC Card end of line & replacement model details. i am looking for Q02CPU replacement model. Please advice. thanks
Replies
2
Views
126
I have Allen Bradley plcs, I have had Circuit breakers and other automation equipment in the past. There's no solid buyers local. How much do you...
Replies
2
Views
202
can anyone has a good program to learn plc programming online. i have the basic looking into improve my skills thanks
Replies
1
Views
144
I want to monitor a couple signals in a place where there is no PLC but there is ethernet. I know I can use an AENTR or Flex I/O and a module but...
Replies
21
Views
779
Back
Top Bottom