Noticed on the PLC5 webpage there are a number of collisions reported. Reset the counters and can watch it rise.
This PLC5 is only communicating with a supervisory L71(EN2T). The EN2T is not reporting any collisions. The L72 is both reading and writing to the PLC5 through multiple messages. Both are connected to our facilities' VLAN.
Not a networking expert here but I understand collisions are not good and should not be seeing any. ??
I also noticed that all our PLC5's, on the network, are set on 10M/half. Not sure the reasoning here other than its older Ethernet technology?? IT did move this one to another switch port earlier this year due to a network infrastructure update. Included new copper run.
Temporarily set this one to 100M/Auto and it seemed to talk ok but was still getting collisions.
What do I need to look at to help reduce collisions?
Thanks!
This PLC5 is only communicating with a supervisory L71(EN2T). The EN2T is not reporting any collisions. The L72 is both reading and writing to the PLC5 through multiple messages. Both are connected to our facilities' VLAN.
Not a networking expert here but I understand collisions are not good and should not be seeing any. ??
I also noticed that all our PLC5's, on the network, are set on 10M/half. Not sure the reasoning here other than its older Ethernet technology?? IT did move this one to another switch port earlier this year due to a network infrastructure update. Included new copper run.
Temporarily set this one to 100M/Auto and it seemed to talk ok but was still getting collisions.
What do I need to look at to help reduce collisions?
Thanks!