I have a failing Panelview connected to a SLC 5/04 over DH-485 using a pair of SLC 500 Link couplers as the PLC and HMI are about 125 feet apart
My plan is to swap out the existing 5/04 and change to a 5/05 and use Ethernet to connect the new HMI to the SLC PLC
I am using the PV Standard to PV Plus 7 conversion guide from Rockwell to pick my new PV hardware and my PV standard is a model # 2711-T10C3X Rev C and FRN 4.48 and is 120 VAC Powered.
My issue is in the conversion guide I can only find 2711-T10C3 and not a model with the X at the end nor can I find anything in the Panelview standard on what the X means but it has to be fairly common because I was looking on eBay for spares as we have several of the machine purchased at the same time originally and on eBay I found 6-7 units with the part # 2711-T10C3X.
Just wanted to do some checking before I order the new PV+ 7
My plan is to swap out the existing 5/04 and change to a 5/05 and use Ethernet to connect the new HMI to the SLC PLC
I am using the PV Standard to PV Plus 7 conversion guide from Rockwell to pick my new PV hardware and my PV standard is a model # 2711-T10C3X Rev C and FRN 4.48 and is 120 VAC Powered.
My issue is in the conversion guide I can only find 2711-T10C3 and not a model with the X at the end nor can I find anything in the Panelview standard on what the X means but it has to be fairly common because I was looking on eBay for spares as we have several of the machine purchased at the same time originally and on eBay I found 6-7 units with the part # 2711-T10C3X.