#61 |
Member
|
OK, now I see that the engineering units are Hz. I like Hz over RPM too only I usually say revolutions per second or rps.
Another question I have is why does the model start at about 27 Hz instead of zero like the PV? Also, I can see that the controller is not controlling the speed directly. There must be a drive in between the controller and the motor. In torque or current mode the torque/ angular acceleration is proportional to the current to the motor. Your system appears to be in velocity mode where the velocity is proportional to the voltage to the drive. When tuning a motor in velocity mode we usually excite the motor with an output that looks like a W or M depending on the direction. When tuning is torque mode we output a pulse that stays on until the motor reaches a desired speed or travels a distance limit and then we must brake by outputting a negative pulse to decelerate. We usually get better performance by skipping the velocity loop inside the drive.
__________________
"Living is easy with eyes closed, misunderstanding all you see...." Strawberry Fields Forever, John Lennon |
![]() |
![]() |
#62 | |
Member
![]() ![]() Join Date: Jun 2020
Location: Melbourne
Posts: 38
|
I'm unsure why the model starts there. I think it was related to the little step in the ramp up. I believe DestinationUnknown is already working on a patch for me :P
This was just a really rushed test last week, i think i chucked the pump in manual from SCADA and hit run but changed the SP halfway or something.. Ill have a more calculated attempt next week. Pump is being driven by a powerflex 755 with VelocityMode and AccelTime =20s. Slow ramp is so the operators can run it in manual from the drive HIM without sloshing the water around too much. I'm not too concerned about a responsive ramp up, can probably occur over 5 mins if required. I'm only expecting the system to start / stop once a day minimum. Quote:
I come from a robot programming background so have never actually tuned a process PID loop before :P Last edited by moistcat; August 25th, 2022 at 03:33 AM. |
|
![]() |
![]() |
#63 | |
Member
![]() ![]() Join Date: Jun 2010
Location: Ireland
Posts: 95
|
Quote:
It works by calculating the ambient as an average of the PV before the step in CV, and as you can see it doesn't work with Ramps. So it should work for you but try editing the data so that the CV goes from 0 direct to 30, and make sure you have the latest version of pytunelogix. As I said this is a specific limited tuner, it's intended purpose is for tuning based on a 0-10% or 0-20% bump test/process reaction curve. If you want an open loop Ramp Tuner, Closed loop tuner or an Adaptive Tuner you will have to open your wallet. ![]()
__________________
same same, but different... Github: https://github.com/Destination2Unknown YouTube: https://www.youtube.com/channel/UCjw...hVY32I2q2JZnBQ Last edited by destination unknown; August 25th, 2022 at 09:16 AM. |
|
![]() |
![]() |
#64 | |
Member
![]() ![]() Join Date: Jun 2010
Location: Ireland
Posts: 95
|
Quote:
Code:
run at minimum pump speed for a period (to get stable flow) ramp manually at a defined ramp rate switch the PID to Auto when within controllable bounds
__________________
same same, but different... Github: https://github.com/Destination2Unknown YouTube: https://www.youtube.com/channel/UCjw...hVY32I2q2JZnBQ |
|
![]() |
![]() |
#65 | |
Member
|
Quote:
You need to find out why the model starts at 27 Hz. The model state should be initialized to the actual initial state. I think the 27 is a "left over" from the temperature auto tuning where the initial temperature is 27 degrees C. The auto tuner should set the estimated state to as close to the actual state as possible. Always. destination unknown should make the initial estimated state equal to the actual initial state. This includes the PV and the rate of change in PV or PV/dt.
__________________
"Living is easy with eyes closed, misunderstanding all you see...." Strawberry Fields Forever, John Lennon |
|
![]() |
![]() |
#66 | ||
Member
![]() ![]() Join Date: Jun 2010
Location: Ireland
Posts: 95
|
Quote:
This is just a basic tuner by design... Quote:
Adaptive.jpg SOPDT Adaptive: SOPDT Adaptive.jpg I was originally going to just release the Adaptive AutoTuner but most of the commercial PID tuners don't even have that. Nor do they have Live tuning and some don't have closed loop tuning. And I So depending on interest levels, I may go down the sponsorware route and release it that way instead.
__________________
same same, but different... Github: https://github.com/Destination2Unknown YouTube: https://www.youtube.com/channel/UCjw...hVY32I2q2JZnBQ Last edited by destination unknown; August 26th, 2022 at 12:26 PM. |
||
![]() |
![]() |
#67 | |
Member
|
Quote:
If you get some traction with your program, I would add more features or abilities. BTW, does the program "know" it needs to update or improve the model? The reason I ask because in one example the program makes a step change and gets to the set point but what if the system changes? How do you know the new model better than the last? I have some ideas. I would keep a sum of the SSE for the last n samples. When the SSE starts to grow its time for another update. The problem is that is the system is slowly changing, then there isn't enough dynamic data to find the new and better gains and time constants. This is the problem with RLS (recursive least squares). The program needs to be very careful about auto updating.
__________________
"Living is easy with eyes closed, misunderstanding all you see...." Strawberry Fields Forever, John Lennon |
|
![]() |
![]() |
#68 | |
Member
![]() ![]() Join Date: Jun 2010
Location: Ireland
Posts: 95
|
Quote:
First is the pytunelogix, which is a python package for tuning via step response, and this will stay in its current form (bar bug fixes) Second is the adaptive tuner, which can tune from any response (step, ramp, closed loop etc..) In the Adaptive tuner, the tuner is triggered by a transition from Manual to Auto or a Setpoint Change. Also there are constraints on the minimum time and/or minimum number of models found before updating the PID gains. It has two modes: passive -> which just records the models and tuning values active -> which updates the gains on the fly. Once at steady state the PID should be able to handle any smaller disturbances, or you could use an external trigger to re-model if there is known point of change in the system. The minimizer handles which model to use but some supervision is required... Any further and you are verging onto MPC territory rather than PID control.
__________________
same same, but different... Github: https://github.com/Destination2Unknown YouTube: https://www.youtube.com/channel/UCjw...hVY32I2q2JZnBQ |
|
![]() |
![]() |
#69 | |||
Member
|
Quote:
Quote:
There really isn't a need for the FOPDT unless you truly have a FOPDT, and you know there must be more than one time constant in the system. You can try many models and use the one with the lowest SSE. Quote:
The bias/feed forward would change after every change in the set point or if the ambient temperature changes. The advantage would be less integator windup or maybe none, a faster response and dead time would be less of an issue. Yes, feed forwards a way of predicting the output based on a model. MPC is a whole different ball game. There are no controller gains and time constants, but a model is required and even more important. Which minimizer do you use? I use Nelder-Mead for its simplicity and its ability to work without finding derivatives. My second choice is Levenberg-Marquardt. L-M works well on real data. Next comes Powell's. Others that you see mentioned are congruent gradient and BFGS. Both don't work well with real data. When I use Nelder-Mead on the hotrod.txt data the minimum SSE is found after 764 evaluations and 452 iterations. Some iterations require 2 evaluations.
__________________
"Living is easy with eyes closed, misunderstanding all you see...." Strawberry Fields Forever, John Lennon |
|||
![]() |
![]() |
#70 | |
Member
![]() ![]() Join Date: Jul 2022
Location: FrozenHell
Posts: 79
|
Quote:
Here the models, SSE and models results for hotrod Model: W(s) = 3,77142857142857/ ((170,2864769*s+1)* (36,0195267*s+1)* (14,57362541*s+1)* (11,51468826*s+1)) SSE = 299,679587391752 File: HR_4OL.xls Model: 877377,03521654*y + 192258,238321364*y + 11483,3455339285*y + 233,022931851044 *y + y = 3,78047288925465 * u + 76,0996287592855 Or 172,853900269076 y3+y3 = 3,78047288925465 * u + 76,0996287592855 27,5507588534603 y2+y2 = y3 25,3508367317336 y1+y1 = y2 7,26743599677449 y+y = y1 SSE = 226,249328593724 File: HR_4OL_plus_C.xls Model: W(s) = 3,77143 e^(- 20,2327017093169*s) / ((168,718641620594*s+1)* (43,2951553813117*s+1) SSE = 328,620727080502 File: HR_SOPDT.xls destination unknown post 48 model Model: W(s) = 3,78 e^(- 20,73*s) / ((170,861144225725*s+1)* (40,5430557742748*s+1) SSE = 539,305857016416 File: HR_SOPDT_DU.xls Peter, can I ask you to show the result of your model? Last edited by MaxK; August 29th, 2022 at 10:28 PM. |
|
![]() |
![]() |
#71 | |
Member
![]() ![]() Join Date: Jul 2022
Location: FrozenHell
Posts: 79
|
Quote:
![]() Any way All our models are approximate, nor of them are exact. The most common model mismatch is “forgetting” about the actuator. Last edited by MaxK; August 29th, 2022 at 10:36 PM. |
|
![]() |
![]() |
#72 | ||
Member
![]() ![]() Join Date: Jul 2022
Location: FrozenHell
Posts: 79
|
Quote:
For example: if plant include transport devices you have to know if it can change it speed, i.e. dead time, so you should make decision about your system design: to find safest PI parameters, or find several groups of parameters and apply them according to conditions, or something else. Quote:
So I've got the question: How to determine which PI controller settings are best? Or what is the PI-controller settings selection criteria? To make it more funny, I'll attach the curves of your model with the PI settings from post 48 http://www.plctalk.net/qanda/showpos...2&postcount=48. The response to setpoint change is pretty good(but it is not exactly) ... but what about the response to the step disturbance? |
||
![]() |
![]() |
#73 | |
Member
|
Assuming you want the SSE for the hotrod.txt data.
Code:
RMS error = 0.436 final_simplex: (array([[ 3.75741204, 0.68461421, 2.84927027, 77.84024028, 0.35401924], [ 3.75741276, 0.68461511, 2.84926905, 77.84016508, 0.35401852], [ 3.75741085, 0.68461181, 2.84927089, 77.84033032, 0.35402135], [ 3.75741199, 0.68461453, 2.84926966, 77.84023678, 0.35401922], [ 3.75741296, 0.68461419, 2.84927032, 77.8401676 , 0.35401904], [ 3.75741189, 0.68461419, 2.84927023, 77.84025638, 0.35401937]]), array([250.31414491, 250.3141476 , 250.31414762, 250.3141638 , 250.31416494, 250.31416562])) fun: 250.31414490854445 message: 'Optimization terminated successfully.' nfev: 764 nit: 452 status: 0 success: True x: array([ 3.75741204, 0.68461421, 2.84927027, 77.84024028, 0.35401924]) The open loop gain = 3.757 PV/%CO Time constant 0 = 0.685 minutes Time constant 1 = 2.849 minutes Ambient PV = 77.840 in PV units Dead time = 0.354 Time units are the same as provided in input file The closed loop time constant = 0.285 The controller gain = 1.472 %CO/unit of error The integrator time constant = 3.534 minutes The derivative time constant = 0.552 minutes Quote:
So how do you make use of a model that uses the fourth derivative? PLCs only have a PID so the fourth order model is useless IF USING A PLC. I have provided the answer in a previous post on this topic. JRW once called me arrogant. No, I can really derive the tuning equations for just about anything. I have posted the derivation for the controller gains for SOPDT many times. What people need to realize is that everything responds as a function of exponents, sins and cosines. What gets trick is that time constants are not always constant ( I wrote and articles about that ) and gains are not constant in non-linear systems. Sometimes the models get to be more complex and linear Laplace functions are not good enough. I prefer differential equations because they can be used for almost anything.
__________________
"Living is easy with eyes closed, misunderstanding all you see...." Strawberry Fields Forever, John Lennon |
|
![]() |
![]() |
#74 | |
Member
![]() ![]() Join Date: Jun 2010
Location: Ireland
Posts: 95
|
Quote:
If you are constantly updating the model and subsequently the gains, it's almost a sudo MPC. There are plenty of options for future features. Nelder-Mead, it has been the most consistent.
__________________
same same, but different... Github: https://github.com/Destination2Unknown YouTube: https://www.youtube.com/channel/UCjw...hVY32I2q2JZnBQ |
|
![]() |
![]() |
#75 | |
Member
![]() ![]() Join Date: Jun 2010
Location: Ireland
Posts: 95
|
Quote:
__________________
same same, but different... Github: https://github.com/Destination2Unknown YouTube: https://www.youtube.com/channel/UCjw...hVY32I2q2JZnBQ |
|
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Slow Acting Long Time Interval PID Tuning | GrizzlyC | LIVE PLC Questions And Answers | 141 | March 30th, 2021 07:04 AM |
PID tuning methods | OysterMan | LIVE PLC Questions And Answers | 4 | March 21st, 2021 11:59 AM |
Micrologix 1400 Timed Proportioned Output PID Tuning | Paul Begley | LIVE PLC Questions And Answers | 3 | January 13th, 2014 05:26 PM |
PID Tuning and Process Modeling | kdcui | LIVE PLC Questions And Answers | 14 | October 15th, 2009 02:27 PM |
PLC PID Auto Tuning Problem | monet | LIVE PLC Questions And Answers | 6 | May 26th, 2009 10:50 AM |