Quantum to Siemens comms over profibus
I have a piece of equipment with control split between two PLCs. A quantum 434, and a Siemens S7-300, communicating via profibus. I have a prosoft protalk Q in the quantum rack, handling the profibus comms for the Quantum.
Does anyone have any experience with these? I am trying to read the current configuration, and figure out how address 400001 is directed to DB41 Word 6. So I can add registers in the Quantum, a new DB in the Siemens and direct the data back and forth. |
![]() |
![]() |
#2 |
Lifetime Supporting Member
![]() ![]() Join Date: Nov 2006
Location: UK
Posts: 6,656
|
My interpretation of the Quatum documentation is that the 400001 is a reference to the Inputs/Outputs used between the two plcs - the data being written to/from these areas will depend on the program in the plcs.
Doc reference: https://download.schneider-electric....33003471K01000 Caveat - I have never used a Quantum plc
__________________
S7-300 to 1500 conversions done - email (minus the spam) to spams7conversions@hotmail.com |
![]() |
![]() |
#3 |
Member
![]() ![]() Join Date: Feb 2020
Location: texas
Posts: 4
|
The 400001 address is the analog output register for the quantum. 300001 analog in.
400001 is writing to a dbw in the Siemens plc, doing so over profibus. The configuration for what modicon output writes to what Siemens input is in the prosoft protalk q card. Normally, id just connect to it, and just figure it out through trial and error, but this piece of equipment runs 24/7 and i won't get any scheduled time with it until December. Im hoping someone has encountered one of these cards before, and can give me some direction. |
![]() |
![]() |
#4 |
Lifetime Supporting Member
![]() ![]() Join Date: Jul 2016
Location: Manchester
Posts: 460
|
The last time I used a prosoft device, they had stand alone software to configure the device. (Mine was installed in a control logix rack).
Just connect an upload the config. The software was free to download from the prosoft website. |
![]() |
![]() |
#5 |
Member
![]() ![]() Join Date: Feb 2020
Location: texas
Posts: 4
|
Were you able to upload while it was running? I haven't found anything in the documentation if uploading will interrupt the communication or not.
|
![]() |
![]() |
#6 | |
Lifetime Supporting Member
![]() ![]() Join Date: Jul 2016
Location: Manchester
Posts: 460
|
Quote:
However, unless you have the original config file, the upload will be uncommented. Not impossible to work with, an if it's a simple system not too big a deal. You can not download a configuration whilst running. The download stops communication. |
|
![]() |
![]() |
#7 |
Lifetime Supporting Member
![]() ![]() Join Date: Jul 2016
Location: Manchester
Posts: 460
|
Also, remember if reading data from a siemens PLC. They byte swap.
|
![]() |
![]() |
#8 |
Member
![]() ![]() Join Date: Feb 2020
Location: texas
Posts: 4
|
Exactly the information I came here for, thank you so much.
|
![]() |
![]() |
#9 | |
Member
![]() ![]() Join Date: Nov 2020
Location: United States
Posts: 1
|
Quote:
What should I Do?? |
|
![]() |
![]() |
#10 |
Member
![]() ![]() Join Date: Oct 2020
Location: Korea
Posts: 11
|
I have two Prosoft gateways between S7-400 and Schneider Quantum PLC.
I have finally succeeded in communicating between them. 4x in Quantum and Prosoft is called as Holding register. It seems Analogue as word. It is important that 4x register in Quantum and internal address in Prosoft should match each other. 40101 in Quantum is 100 at internal address of prosoft gateway. 40101-40001 becomes 100. Prosoft gateway can easily recognize S7 PLC by putting the target address of S7 PLC. |
![]() |
![]() |
#11 | |
Member
![]() ![]() Join Date: Nov 2020
Location: Dallas
Posts: 1
|
Quote:
Our goal is to support our customers from pre-sales through the entire life-cycle of Quantum PLC with. |
|
![]() |
![]() |
#12 | |
Member
![]() ![]() Join Date: Apr 2021
Location: United States
Posts: 1
|
Quote:
a search engine that has an out-of-date listing for this site a mistyped address you have no access to this page The requested resource was not found. An error has occurred while processing your request |
|
![]() |
![]() |
#13 | |
Member
|
Quote:
The specification states that Profibus data should be sent over the bus using big endian. If the receiving device is a little endian device then it should automatically swap the data correctly for the user. This is one of the things I hated about early Profibus implementations in the North America. Many claimed to be profibus compatible without ever going to the PTO lab and being verified. Make sure your devices have a Profibus certification.
__________________
"Living is easy with eyes closed, misunderstanding all you see...." Strawberry Fields Forever, John Lennon |
|
![]() |
![]() |
#14 | |
Member
![]() ![]() Join Date: Oct 2022
Location: Dallas
Posts: 1
|
Quote:
The Siemens Smart MCC with integrated PROFIBUS is capable of being controlled by every major supplier of PLC today. Of course, the most powerful option is to |
|
![]() |
![]() |
#15 |
Member
![]() ![]() Join Date: Nov 2022
Location: Cape town, Australia
Posts: 2
|
Yes, you are right Thomas.
|
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
profibus network between Siemens S5 and S7 PLC | Leonardo | LIVE PLC Questions And Answers | 12 | February 19th, 2021 06:25 AM |
Strange MPI comms issue on HMI (Siemens) | uptown47 | LIVE PLC Questions And Answers | 2 | January 13th, 2016 05:13 AM |
Profibus Master/Slave comms | Revver | LIVE PLC Questions And Answers | 6 | September 23rd, 2015 04:13 AM |
Extract profibus adres on profibus failure (Siemens S7) | genesisfm | LIVE PLC Questions And Answers | 3 | May 10th, 2010 10:49 AM |
Siemens WinCC and S7-315 Comms | Coops | LIVE PLC Questions And Answers | 5 | April 7th, 2008 07:35 AM |