Mas01

Member
Join Date
Oct 2020
Location
Leicester, England
Posts
1,105
M367 is a press-button on the PLC screen, X212 and X213 are PHYSICAL buttons on a control panel - you press them with your finger. What does the SET and RST do on the right-hand side?
Thanks

Capture2.PNG
 
SET turns the contact "ON" and RST (Reset) turns it off.
The contact will stay on even when the logic in front of it goes false
so when the logic driving the "Output" is true it sets it to "ON" , it then stays on even when the logic goes false until it is reset by a "TRUE" condition in the following rung that resets it.
The only caveats are that in PLC's there are retentive memory and none retentive memory, so if the PLC is switched off a coil or contact that has been set to ON will stay on when the PLC is switched back on if the bit memory is retentive, however, if it is a non retentive memory it will be reset on the PLC being switched back on and will require a SET rung to go true to switch it back on.
However, I'm concerned about the logic you show, because the selection bit M367 is on to select the pump, this means if the selection bit is turned off the pump continues to run and cannot be stopped unless there is another reset of the pump elsewhere.
 
Set/Reset is like latch /unlatch. Push motor start button turns on vac pump and holds it on. Push motor stop turns vac pump off.
 
SET turns the contact "ON" and RST (Reset) turns it off.
The contact will stay on even when the logic in front of it goes false
so when the logic driving the "Output" is true it sets it to "ON" , it then stays on even when the logic goes false until it is reset by a "TRUE" condition in the following rung that resets it.
The only caveats are that in PLC's there are retentive memory and none retentive memory, so if the PLC is switched off a coil or contact that has been set to ON will stay on when the PLC is switched back on if the bit memory is retentive, however, if it is a non retentive memory it will be reset on the PLC being switched back on and will require a SET rung to go true to switch it back on.
However, I'm concerned about the logic you show, because the selection bit M367 is on to select the pump, this means if the selection bit is turned off the pump continues to run and cannot be stopped unless there is another reset of the pump elsewhere.
Once again, many thanks (and BrianD, too).
I asked the rig user how the pump is switched off once it's running. He said if the pump's running, you need to click on the PLC button (M367) again and then press the physical STOP pushbutton (X213).
To test this out, we started the motor (by clicking PLC button M367, then pressing the START p/b).
I then pressed the PHYSICAL STOP button X213...outcome...motor kept running.
Then we clicked M367 again and then pressed the physical STOP button X213...the motor stopped.


Thank you, appreciate the help.
 
...
To test this out, we started the motor (by clicking PLC button M367, then pressing the START p/b).
I then pressed the PHYSICAL STOP button X213...outcome...motor kept running.
Then we clicked M367 again and then pressed the physical STOP button X213...the motor stopped.




By "clicked ... M367," do you mean "held M367" while you pressed the STOP (X213)?


Is M367 a momentary bit? It seems from the behavior that that is the case.



But if M367 is not a momentary, then what assigned a 0 to it after it was clicked for the START sequence?
 
Because M367 is controlled via the HMI I suspect it is set in the HMI as a "ALTERNATE" (ON/OFF or toggle) so pressing it once sets it pressing it again resets it to off. It would not make sense to hold a button on an HMI as I think most will only allow one button to be pressed at a time (note: I believe the screen is a touch screen and most will only allow one touch area at a time in run mode). In saying that it is only a guess as there is also another function where rather than using standard built in functions for a button there is also a script function so anything is possible for example, on the start button it could run a script that not only set the start bit but reset the select bit M367.
 
By "clicked ... M367," do you mean "held M367" while you pressed the STOP (X213)?
No - I clicked on M367 first (when 'active' it goes from a dull colour to bright green), then pressed the physical STOP p/b.

It appears that when the physical p/b is pressed (START or STOP), M367 is reset (goes from bright green to dull again).
 
Because M367 is controlled via the HMI I suspect it is set in the HMI as a "ALTERNATE" (ON/OFF or toggle) so pressing it once sets it pressing it again resets it to off. It would not make sense to hold a button on an HMI as I think most will only allow one button to be pressed at a time (note: I believe the screen is a touch screen and most will only allow one touch area at a time in run mode). In saying that it is only a guess as there is also another function where rather than using standard built in functions for a button there is also a script function so anything is possible for example, on the start button it could run a script that not only set the start bit but reset the select bit M367.
Hi, In my case, it's not touch-screen (although I did use the word 'screen' in post #1, apologies). It's just a PC with a mouse pointer. Not sure what causes M367 to reset, but (as mentioned in the reply above) it appears to be linked to pressing either of the physical push-buttons.
 
Last edited:
Soft Got is almost the same as GT Designer so I expect it has the same functions so they could be using a script to set the start bit and at the same time reset the select bit. I really do not see the point in the vac pump select unless there is more than one, then you would normally leave it selected i.e. on for one pump or off for another pump. i.e. duty 1 or 2. Putting the M367 in the reset line does not make that much sense if the bit is reset on a start a bit confusing for the operator if he selects the pump bit M367 then press start but if he wants to stop it he has to press the enable bit again before he stops the pump.
 
Soft Got is almost the same as GT Designer so I expect it has the same functions so they could be using a script to set the start bit and at the same time reset the select bit. I really do not see the point in the vac pump select unless there is more than one...
There's 3 vac pumps. Each has its own Mxxx on the PLC, but they all use the same physical START/STOP pushbuttons to turn them ON/OFF.
 
Ah.. now I understand, that's where the more complete the information given by OP's helps posters to give more accurate replies.
I'm wondering if they select more than one pump enable more will start or have they interlocked the pump enables so pressing the enable for pump 1 resets the enables of pump 2 & 3 and so on.
 
Ah.. now I understand, that's where the more complete the information given by OP's helps posters to give more accurate replies.
I'm wondering if they select more than one pump enable more will start or have they interlocked the pump enables so pressing the enable for pump 1 resets the enables of pump 2 & 3 and so on.
My apologies once again. I wish I were more knowledgeable to realise the significance of mentioning the other pumps.
As for how the pumps are used, vac 1 then vac2 then vac3 are turned on in that order (so all 3 are now on) . On top of that there are boost pumps, to get us as close as possible to a perfect vacuum (0 Torr)
 
Yep I totally understand, the idea of the enables is to use only the Two stop & start buttons but allow starting & stopping of individual ones even though it is unlikely you will run with less than 3 pumps. Not sure why they went for this approach as 3 enables & 2 buttons = 5 whereas 3 stop/starts = 6, not much of a saving, however, I suppose there could be some other reason.
 
Yep I totally understand, the idea of the enables is to use only the Two stop & start buttons but allow starting & stopping of individual ones even though it is unlikely you will run with less than 3 pumps. Not sure why they went for this approach as 3 enables & 2 buttons = 5 whereas 3 stop/starts = 6, not much of a saving, however, I suppose there could be some other reason.
Yes, I think that's the idea, it's some kind of space saving probably. There's 3 vac boost pumps, making a total of 6 vac pumps. One thing's for sure...the physical START/STOP pushbuttons have had a lot of use, and have definitely seen better days.
 
Last edited:

Similar Topics

Sorry for the basic question... I've had a look through the Q68AD-G (analogue input to digital converter), and I'm trying to find out if the...
Replies
11
Views
3,047
Hi, can anyone help? Complete novice here GXDev/SoftGOT/GTDes3 I've had a question from a colleague asking me 'how does the PLC calculate the...
Replies
9
Views
1,852
GTDes3, On all the tabs where the HMI screens are defined, each tab contains the words "(Front+Back)". Anyone know what this means? Thanks
Replies
1
Views
1,162
I've got a bunch of alarms in GT designer3 and they are "mapped" to M parameters, eg M277. What does M signify? Thanks
Replies
4
Views
2,248
Back
Top Bottom