Hi, I would like to know how to get the value/data from Schneider power meter PM5350 through RS485 by using Omron CP1E? Is that possible or you guy has any idea?
 
What is the complete part number of the CP1E?
The CP1E does not accept the communication option boards.

Some models have a built in RS232 port.
If your unit has the RS232 port, you will need a RS232 - RS485 converter.

Serial communication instructions are RXD and TXD.
Actual PLC program would depend on how the power meter transmits the data.
 
Very likely the Power meter would support Modbus protocol.
I am not sure if the CP1E has the EasyModbus Master functionality available
 
Thank for replying my post.

My PLC module is CP1E-E30DR. By the way, I have using CJ1W-CIF11 as RS-232 to RS485 convertor. If i want to get a value from Schneider power meter through RS485, how to program it?

Can share with me the simple ladder program for getting the data from PM5350?
 

Similar Topics

Hello. I have a problem with omron sysmac cp1e controller delayed start. The controller has been working on the punch press since 2016. Recently...
Replies
1
Views
755
Hi, I need to communicate omron CP1E PLC with SCADA to get the status of the machine. There is no etherent port available but an empty expansion...
Replies
2
Views
1,593
Hello... I remove one CP1E from old useless machine and I would like to use it with something else....but it is locked/have no pass/....How can I...
Replies
0
Views
1,436
hi all i have used a real time clock to turn on a bit after 1 month. the plc was off for this whole month and when i turned on the plc after a...
Replies
2
Views
1,414
We had a CP1E go bad (power issue). Installed spare and could not get it to communicate to our motion drive via add on RS485 card. Tried...
Replies
5
Views
1,480
Back
Top Bottom