Even though you did not supply the actual values, I am pretty sure that @LD nailed it on the values:
  • It appears the Modbus receive buffer and S7-1200 Reals are both MSB-first, so a swap is not necessary
  • A range of 35-65 is reasonable for pressures and temperatures in any system of units.
The image below shows a minimal implementation of Example 2 from the link that @Lare supplied, for the first five pairs of words from the OP; OP will of course have to provide their own size for the [store] array in the "COP" FC.