Hello All
I'm trying to write a Dint from a Compact Logix 5069-L306ER and a 2080-LC20-20AWB.
I was able to get a CIP Data Table Read to function as expected.
However I am unable to get a CIP Data Table Write to work.
I'm seeing error

16#0005
Error Test:Class or instance not supported


Path is 3,192.168.1.12


Not sure what I'm missing and I'm not finding much information online.
I'd appreciate any advice or suggestions.
Thanks
Mrdegold

01162022A.JPG 01162022B.JPG
 
After I posted this I walked away. Which is when I came up with checking that my destination address in the Micro 820 was set as a Global Variable.
So I created a New Dint Tag in the Micro 820 made sure it was a
Global Variable.

Bingo MSG Write started working as exected.
Sorry for the trouble
mrdegold
 
Thanks for the followup !

The target tag's folder/scope is a classic mistake, which I have made myself numerous times.
 

Similar Topics

The Ethernet has 3 pieces of PLC5 processors (PLC5-40E), for easy explanations, we name A,B and C. All pings are OK and RSLogix5 can connect all...
Replies
13
Views
4,823
Hi All. I can write an N7 value to a modbus register in an Automation Direct Servo but I can't read a holding register to an N7 address. I've...
Replies
3
Views
1,892
Hello All, I've got a Compactlogix (v30.11) communicating to a SLC 5/04 over ethernet (CL side) through a AN-X2-AB-DHRIO module to DH+ (SLC...
Replies
4
Views
2,308
Got a trouble call from a customer this AM that one of the compressor systems is getting its setpoint overwritten and mode (local/remote)...
Replies
4
Views
2,069
Hello, New to the forum here, and to the controls industry. I am trying to do the following: Read and Write to a 5204-DFNT-PDPMV1 ProLinx...
Replies
0
Views
1,878
Back
Top Bottom